By all means, stick with the NEC, whatever it requires. But you are going to have to read the fine print when the drive is much larger than the motor because the branch circuit protection is not protecting the motor. It is, instead, protecting the AC drive. The drive protects the motor for overload, overcurrent, and ground fault.