1769-l32E Message

brown2121

Member
Join Date
Mar 2017
Location
buffalo
Posts
5
I am trying to do a CIP Read to a 1769-L32E from a 1769-L30ER but I keep getting a 16#0001 error.

path = LocalENB,2,10.10.2.15,2,0
 
So looking at the suggested thread I changed my path to the following and I am still getting the error.

path = LocalENB,2,10.10.2.15,1,0
 
Are both PLCs on the same subnet?
If yes, can you put your PC on that subnet and ping both units?
If no, Is there routing setup to allow them to talk?
 
Your path should read something like this:
1,1,2,10.10.2.15,1,0

1,S1,2,xxx.yyy.zzz.www,1,S2
Where:
1 is the backplane for the first chassis (the clx backplane always uses 1)
S1 is the slot of the 1756-ENBT in the first chassis (the first position on the left is 0, second 1,...)
2 is to go outside to the Ethernet (always 2)
xxx.yyy.zzz.www is the IP address of the 1756-ENBT in the second chassis
1 is the backplane for the second chassis (always 1 for clx)
S2 is the slot of the CLX in the second chassis (starting from left the first position is 0, second 1,...)
 

Similar Topics

I just found two old 1769-L32E controllers in the plant that I cannot go online with using my version of Studio 5000 (30.14). I've reached out to...
Replies
5
Views
1,879
Has anyone experienced the following issue on RSLogix5000 (currently on V16) I have a PLC program that has been running on a site for a number...
Replies
5
Views
1,581
Hello; We have an Allen Bradley compact logic processor at an auto glue kitchen of corrugator machine which connected with AB HMI. Normally to...
Replies
5
Views
2,420
Hello all, I have a small issue that I'm sure is something I overlooked but I'm stumped so I'm hitting the old Interweb to ask for help. On my...
Replies
11
Views
3,890
Using Rslogix 5000 Data Access manual as a reference I keep getting 'Service Not Supported' response when using symbol instance addressing to...
Replies
2
Views
1,545
Back
Top Bottom