Hello,

I have a cp1h-y20dt-d (sinking output) plc supposedly to be wired to a servo controller. The pulse control method is Pulse/Direction. I've did some manual research on the PLC and found the following diagram:

Untitled.jpg

Since the diagram above doesnt show which terminals does it connect to in the CP1H side circled red, I want to ask if those connections belong to the following diagram?

Untitled1.jpg

If so, assuming im planning to use only Pulse Output1 (Pulse/Direction method) from the PLC side, is the connection from the first diagram no.1=CCW0- , no.2=CCW1- , no.3=COM (connected to -ve)

*Note: these diagrams are from omron's manual SYSMAC CP Series CP1H-X40D_-_ CP1H-XA40D_-_ CP1H-Y20DT-D CP1H CPU Unit

Your replies would greatly help.

Thanks and best regards,
Danny
 
Welcome to the forum.

You are correct.

I was not sure about the hardware side for CW/CCW or Pulse/Direction but that is set in either the PULS or PLS2 instruction.

Best of luck on your project.
 
For PULSE output 0 using PULSE plus DIRECTION configuration you connect CW0+ [Pulse] to the pulse input of your servo and CW1+ [Direction] to the direction input of your servo. Then connect COM[-] to both CW0- and CW1- terminals.
 
Welcome to the forum.

You are correct.

I was not sure about the hardware side for CW/CCW or Pulse/Direction but that is set in either the PULS or PLS2 instruction.

Best of luck on your project.

For the 2nd diagram, what is the difference between a Special Pulse Output (00 to 03) and a Normal pulse output (04-07)?
 
Pulse/Direction outputs 0 and 1 are Line Driver Outputs rated up to 1MHz.
Pulse/Direction outputs 2 and 3 are Sinking Outputs rated up to 1kHz.
If pulse/direction 2 and 3 are NOT configured in the PLC Setup then they may be used as "Normal" ON/OFF outputs in the program.
 
Pulse/Direction outputs 0 and 1 are Line Driver Outputs rated up to 1MHz.
Pulse/Direction outputs 2 and 3 are Sinking Outputs rated up to 1kHz.
If pulse/direction 2 and 3 are NOT configured in the PLC Setup then they may be used as "Normal" ON/OFF outputs in the program.

For Outputs 0 and 1 (Line Driver Outputs), I noticed there is no COM to connect for a sinking output, if it were to be connected to a servo controller, it should be a direct connection? As in:

CCW0+ --- PULSE+ (SERVO CONTROLLER)
CCW0- --- PULSE-
CCW1+ --- DIR+
CCW1- --- DIR-

*Note: on the servo controller side there's only these mentioned 4 terminals (pulse+/- and dir+/-)

Is this connection correct?
 
Using Line Driver pulse outputs 0 and/or 1 or Sinking pulse outputs 2 and/or 3 is completely dependent on the pulse input specifications of your servo controller.
You don't specify the manufacturer/model # of the servo you intend to use so it's hard to recommend which ones you should use.
May also be worth checking with OMRON whether the Line Driver pulse outputs will work in a sinking mode. You can always test this out if you have the physical hardware available.
 
Last edited:
Using Line Driver pulse outputs 0 and/or 1 or Sinking pulse outputs 2 and/or 3 is completely dependent on the pulse input specifications of your servo controller.

I see. Based on my servo's manual, the image of the internal circuit shows an open collector type input. Isit possible to link Line Driver Output to an open collector pulse input? Image below shows the open collector type input:

Untitled.png
 
That all depends on your servo model input specifications.
AGAIN you haven't specified the servo model so Contact your servo supplier for more specific info.
If I were doing this I would just hookup the physical components and test if it works.
 

Similar Topics

Hi all, I have to say first that I have no experience with Omron devices, but here's the challenge that I'm facing. I have an Omron CP1H...
Replies
7
Views
1,674
I have a question about SET instruction in Cx-programmer. When condition goes true it is supposed to give value 1. But, my controller is giving 0...
Replies
24
Views
2,245
Hello Sir/Ma'am, Hope you and your family are safe in this Covin-19 Pandemic. One of my client have a machine in their ceramic industry which...
Replies
0
Views
2,593
Hi, I recently had to buy a batch of new electrical components containing 10 PLC Omron Type (CP1H-X40DRA) Apparently stored in store (to be used...
Replies
10
Views
3,463
Hi good day, we have 4 omron cp1h and one pt connected through modbus rs485. Now we try to add some of the inputs to one plc and transfer to...
Replies
1
Views
1,299
Back
Top Bottom