Good Evening,

I am curious to know, if its possible to use PlantPax graphics, face plates in Factory Talk View without utilizing its Add On Instructions (AOI) in the PLC program.
 
Do you mean, can you use certain parts of the graphics and roll your own connections for them behind the scenes? I suppose so, but it would be a lot of work.

Otherwise, no, the graphics require the AOIs to function.
 
Do you mean, can you use certain parts of the graphics and roll your own connections for them behind the scenes? I suppose so, but it would be a lot of work.

Otherwise, no, the graphics require the AOIs to function.

Thank you for the quick reply. Yes, is it possible to use the graphics without using its AOI in the plc program. For example to show motor running on the graphics, is it possible to take a modbus register to indicate the motor is running?
 
Technically, yes that would be possible. But it would be so complicated that you would be better off just copying the graphic and add a color change animation.
 
Hi,

Yes. It may just be easier to use the AOI as it is though. In your example, you would just point the relevant ‘Running’ input condition of the AOI to your modbus address (the AOI only checks for a 1 or 0). The contactor feedback, motor tripped feedback inputs etc. can be turned off as necessary. The AOI can be configured as basic as you need it.
As already mentioned in previous replies, the faceplate graphics can be pretty complicated and cumbersome to work with, so it can be quite time consuming (some of the objects are grouped within groups of even more groups). I have modified several of the standard graphics to suit our applications, but it is not a 5 minute job (is possible, just quite fiddly).

Hope this helps.

Rob
 
Hi,

Yes. It may just be easier to use the AOI as it is though. In your example, you would just point the relevant ‘Running’ input condition of the AOI to your modbus address (the AOI only checks for a 1 or 0). The contactor feedback, motor tripped feedback inputs etc. can be turned off as necessary. The AOI can be configured as basic as you need it.
As already mentioned in previous replies, the faceplate graphics can be pretty complicated and cumbersome to work with, so it can be quite time consuming (some of the objects are grouped within groups of even more groups). I have modified several of the standard graphics to suit our applications, but it is not a 5 minute job (is possible, just quite fiddly).

Hope this helps.

Rob

Thank you for the reply. I understand this job may not be as easily. I am asking this because of a project. Our company is only hired to do the HMI, the PLC programming has been already done. So there is no way we can implement AOI and utilize these graphics. My main objective is to utilize Plant Pax library with just modbuss address and not use their AOI.
 
Hi,

In a nutshell, yes you can use the graphics as standalone objects. However, to strip out all of the (heavily grouped) layers of pre-tagged, and parametrised sub objects, you may find it easier to just make your own. Each of those graphics are made up of several sub groups that control several functions in the PLC and are driven by many more sub AOI groups (Mode/Alarm/Interlocks/Permissives etc.) so you will need to allow quite a lot of time debugging them.

Presumably your modbus signals will still need to be integrated within the PLC code (to ultimately drive the new graphics)?

Rob
 

Similar Topics

I know this can be done, but I can't get the router config right. My goal is to physically connect(using an ethernet cable) a device(PLC, RTU...
Replies
9
Views
976
I haven't had to tune a PID loop in a very long time. It's actually a PI loop for a pulse width modulation s.v. What was the name of that tuning...
Replies
16
Views
4,073
Hello, I have a question regarding the analog output modules on a AB Micro850. I'm not getting an output to my valve and when I put a meter on it...
Replies
2
Views
1,526
Happy new year everyone. This is more of a Electrical engineering question than a PLC one. Can a Motor and a VFD that is rated for 240/480...
Replies
29
Views
9,619
This may be a simple question. I understand the concept and application of analog modules (i.e. Compactlogix) for transducers, and outputs for VFD...
Replies
4
Views
1,990
Back
Top Bottom