Air Enthalpy calcs

saultgeorge

Lifetime Supporting Member
Join Date
Jul 2015
Location
Detroit
Posts
535
Morning, folks. I hope I get some views on this and maybe a reply. I'm reaching out to the best of the best here.
I'm writing logic for some Air Handling Units (AHU's) for a customer that has contracted us to do so. I'm using RS5k v. 20.04
Anyway, to be brief, I need to perform an enthalpy calculation on outside air temp and humidity percent, which are the only 2 values I get into the logic.
If you'll note the 2 links, the equation gives you the result in kJ/kg, which I don't know how to relate to the temp. I am using the one from wiki without steam tables. I have absolutely no problem using the equation in the logic and doing the math, I just don't understand how to use the result. The reason for this routine is that an AHU can use outside air to help with cooling without using the chilled water at certain outside temps. But if the humidity is too high, even though the outside temp is low, say 50, then it would do no good to bring in that air. There will probably be some kind of a comparison I will have to make. I have emailed the engineers that do this and that sent me the links, but no reply so far. Any enlightenment is more than I have now. Thanks in advance, folks. Happy Monday.

https://sciencing.com/calculate-enthalpy-air-6118694.html

https://www.wikihow.com/Calculate-the-Enthalpy-of-Moist-Air
 
It's been too many years since I hade to deal with thermodynamics.

this maybe a stupid question on my part, if you have a humidity limit (not to exceed this value), why not program that into your logic as the determining factor?

just a question and as I said, to many years ago for this calculation but I still have my books.

james
 
I guess I'm not sure what the question is. I assume that the AHU is going to be used with tempering air, and the enthalpy calculation is part of that. Here is one explanation of tempering air: https://www.garagejournal.com/forum/archive/index.php/t-3860.html Some searching by you will yield more results. You might also look at the ASHRAE site.

A couple of notes. First, do some checking on the formula's accuracy over the range of operation you are expecting. These look like empirical formulas, and they may or may not be accurate for your conditions. A check calculation with known accurate results provided by your client would be in order.

Second, note that the moisture content portion of the equation is the humidity ratio, kg/kg. This is not equal to relative humidity (%RH) but is a function of %RH and temperature.
 
Thanks Tom and James. Yes, I have received even more equations from their engineers. They use an on-line type calculator (similar to a mortgage calculator) to do their math. A comment to Tom's reply, that sounds like a good idea, using RH to say yea or nay to using the outside air economizer, but the specs call for enthalpy calculation of the outside air and humidity. I'll keep at it. Really, thanks so much for taking the time to help.
 
Have a look at the functions on the website of oscat.de they are used to make the calcs in a simple way.
and yes it is enthalpy , however the moist will change the enthalpy as it takes more energy to cool moist air, and if the water condenses it even takes more energy.
 
Thank you g.mccormick and shooter. I was given that PDF from Vaisala and those are the equations I'm using to compute the enthalpy in my logic. I then compare outside air enthalpy to return air enthalpy. If outside is more, then no economizer dampers open and no free cooling. Thanks to all for the replies and research and your time.
 
Thank you g.mccormick and shooter. I was given that PDF from Vaisala and those are the equations I'm using to compute the enthalpy in my logic. I then compare outside air enthalpy to return air enthalpy. If outside is more, then no economizer dampers open and no free cooling. Thanks to all for the replies and research and your time.

(y)
You're welcome.
 

Similar Topics

The web abounds with companies claiming they can repair HMIs and other industrial electronics. I am looking for recommendations for companies...
Replies
8
Views
1,224
Hello, I been trying to pull the probe readings from my Metro M400 air gages through a modbus to a plc. I have a connection right now between the...
Replies
1
Views
1,098
Can anyone recommend a Dew point sensor for compressed air with either I/O Link or EtherNet IP Connection. I have found this...
Replies
3
Views
677
Any suggestions on how to repair the power supply GT27-10PWD in the display (GT2508)? Any documentation or place that fixes it? Thanks in...
Replies
2
Views
618
I just replaced a SLC 5/05 last night. 1747-l553/C FRN 10 A couple weeks ago it faulted out while running and going online showed Non volatile...
Replies
19
Views
4,002
Back
Top Bottom