I have an A.B. 5/05 and I get an major fault 1F51H: A Stuck runtime error was detected on an I/O module. This error is non-recoverable.
Can someone help me?
First of all, you need to find which module is causing the fault. Do you have some sort of basic card, serial module or other specialized module in the rack? If I remember correctly, the last time I saw this, the maintenance techs replaced a specialized module without regard to dip switch settings. Another time, the slot number the fault number associated with was one more than the actual module that was bad. That took some time to figure out, and AB's tech support was useless.David
It means there is a error in the communication between the backplane and an i/o module.
The "1F" in 1F51 means that the exact slot cannot be determined.
Try to disable slots one at a time (see S:11 and S:12) and see if the error goes away. Maybe that can pinpoint which module that causes the problem.
Otherwise you may have to exchange modules or the rack to get rid of the error.
Like Jesper said, the slot number cannot be identified.
When the error occur, I can reset it and it goes away for a week or two. So I cannot try to disable slots one a the time.
One other thing that I should mentioned. I have a two rack configuration with the cable between the racks. Do you think that the cable may cause any problems because the second rack is in an other panel (2' away)?
David,
Yes I do have a basic module on the rack. But It has been on the rack since the project start-up and I have had this error since the start-up.
Do you think that the module can be in trouble?
If they share the same power supply, and there is a nice thick earth connection between them, then it would be the same as having the two racks in the same panel.
Is there any special noise generating equipment (very large contactors, relays/solenoids without surge suppressors, VFDs ...) ?
Do people electro-weld without a proper return path for the welding current ?
Unfortunately, if the error is not easily reproducable, then it will be hard to find. I agree with Jesper about possible noise problems. Verify your grounding. This one will be a bugger to find I'm afraid.
David
Hi everyone again ��. I am having a problem rack that has been giving me fits.This time it has a fault that says. a "stuck" runtime...
2,726
I am copying this questions from member E Nabors in the Practice Forum: http://www.plctalk.net/qanda/showthread.php?t=81258 SLC 500 error: "a...
2,088
I have a SLC 500 that looses the program sporadically when powered up. Yesterday we actually were able to retrieve an error from the processor " a...
2,783
Quote A "Stuck" Runtime error is detected on I/O module 3 Un-Quote In a System comprising: SLC 5/01 CPU / 16 Input DC Sink / 8 Output Relay /...
4,610
I have a SLC 5/02 PLC in my office that I use to play around with (beginner)I have been useing this PLC for some time, Im using the 1747-UIC...
7,894