AB FLEX IO Limits
AJZ
Jul 2003
Ontario
265
What are the limits for module use on a AB 1794 FLEX IO system?
I know that the maximum number of modules is eight and the maximum number of I/O points is 256. Based on this info, I can use eight 32point modules. Is that correct?
Also, is there a limitation to the number of input or output modules used?. For example, can I use six 1794-IB32 modules with two 1794-OB32 modules
Adrian
Disclaimer; I have not worked directly with the 32-point I/O modules but I am very familiar with the fundamentals of the 1794 platform.
The physical FLEX bus can support eight modules of any type. Analog, Specialty, 8-point, 16-point, or 32-point, it doesn't matter.
1794 FLEX is a 16-bit I/O architecture, so if you have 32-point modules you will have to logically communicate with them differently than with 16-point ones.
The most important consideration is which network adapter you are going to choose. Only the newest adapters for RIO, DeviceNet, ControlNet, and EtherNet/IP support the 32-point I/O modules, and they do so in slightly different ways.
The EtherNet/IP adapter, for example, allows you to make a logical I/O connection directly to the 32-point module, which is less efficient than a "rack optimized" connection but still works. I think the RIO adapter requires block transfers.
Get the release notes for the network adapter you will be using and they will have information on how 32-bit support is implemented in that adapter.
Here's a 32-bit module compatiblity table, taken from the 1794-IB32 installation manual:
Remote I/O
1794-ASB series E or later
1794-ASB2 series D or later
ControlNet
1794-ACN15 series C, firmware revision 4.1 or later
1794-ACNR15 series C, firmware revision 4.1 or later
Ethernet
1794-AENT series A, firmware revision 2.4 or later
PROFIBUS
1794-APB series A, version 1.1 of the GSD file
ControlLogixTM Family RSLogix5000 programming software, version 11 or later
Just want to confirm that Ken is correct.
Limit still 8 modules.
Correct adapter must be used that supports 32 bit mode.
Thanks, Ken.
I am working on a new system using DeviceNet as the Network. A CLX L61 is the PLC.
Ken, I noticed that you did not list a DeviceNet module in your list. Does that mean I cannot use the 32point modules?
Adrian
Check these technotes for 32 point modules and 1794-ADN:
P20842 - 1794OB32P, 1794IB32, 32 point Flex I/O module and supported adapters.
Q110737688 - DeviceNet: 1794-ADN f/w 2.002 issue with Autoscan and 1794-IB32 or 1794-OB32P
A63745719 - Configuring 32 point discrete Flex I/O on a 1794-ADN DeviceNet adapter
Thanks for those, Control_Conn.
Those knowbase articles are more thorough than the installation instructions that I downloaded. See what happens when we let literature majors do engineer's work ! :)
FLEX is a pretty old architecture and I'm grumpy about the way it works on DeviceNet (complex to map and maintain), but it's a good way to get a lot of I/O in a small space, especially when you connect it up on ControlNet or EtherNet/IP.
Hi How do I configure high and low limits for a number entry I know I can program limits in the PLC to catch this. I have looked into WinCC and...
5,491
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
120
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
161
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
146
Hi, Is it possible to for an RIO with Flex 5000 series module, e.g. 5094-AEN2TR, to communicate with an 1756-L72E processor.
86