PowerFlex 525 and Opto 22

Saulo35

Member
Join Date
Jan 2012
Location
Port Coquitlam, BC
Posts
112
Hi,

Has anybody controlled and monitored a PowerFlex 525 VFD using Opto 22's PAC Control? The client is still undecided between EPIC or staying with SNAP/PAC, but it should be irrelevant since the software will be PCA Control in either case. I have been able to do this with Yaskawa drives over Modbus, but this will be my first time with PowerFlex. Have you used RS485 or Ethernet TCP/IP?

Any pointers will be welcome.

Thank you,
 
The last guy who answered is just spamming the board; he has no "friend" with relevant experience. I'll remove his post in a minute.

In general, use Modbus RTU over RS-485 for this purpose. You get start/stop and reference/feedback control over a simple set of holding registers, and monitor parameter access over another set.

I can't give you advice on the use of EtherNet/IP with Opto-22, unfortunately. There may be some other folks on the Forum who have good information and are not spammers.
 
Today, after I received the Opto 22 EPIC GRV-CSERI-4 serial communication module, I am happy to report that I was able to establish RS-485 communication between the EPIC PR1 processor and the Powerflex 525. I was able to read the drive status. It is undervoltage-faulted, (bit 7), because I am powering it with single-phase 115 VAC instead of 230 VAC. I was able to see the Cmd Fwd/Rev (bit 3) and Rotating Fwd/Rev (bit 4) change as I pressed the reverse direction button on the VFD's front. You just have to add 1 to the register numbers given by Allen-Bradley (i.e. to read the drive status, use 0x2101 instead of 0x2100).
 

Similar Topics

Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
206
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
0
Views
123
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
446
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
4
Views
220
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
282
Back
Top Bottom