question about replacing new servo drive: Kinetix 350

mike3475

Member
Join Date
Feb 2013
Location
brooklyn ,NY
Posts
334
Good morning everyone:
We had burned up Kinetix 350 drives by mistake (put AC 110V in +24V)

the drive configured with existing motion group and ran fine before burned up.
At first we need to configure the same ip address for new drives by keypad input,that is only step we have to do or we have to configure it like new drive step by step followed by its manual?

Thanks!
 
Last edited:
Because the Kinetix 350 is a "CIP Motion" drive, all of its configuration except the IP address comes from the ControlLogix that is running it.

Set the IP address and as long as the firmware is compatible with what's in your ControlLogix project, that should be all the configuration you have to do.
 
today we got new Kinetix350, we only swapped memory module, then it works fine, found out this new drive with firmware reversion is 2.003, i remembered the old bad drive firmware reversion was 2.001, so that means that memory module only stores the IP address,not the firmware,right?
Thanks!
 
I've used dozens of Kinetix 350 drives, but never had to think about the 2097-MEM memory module !

On the Kinetix 300 drives, that module stores all the configuration information for the drive and its indexing features.

On the Kinetix 350, I think all it stores is the IP address, and possibly the absolute position of the encoder at power-down.

It almost certainly doesn't store the drive's firmware; that's got to be in a nonremovable nonvolatile memory chip.
 

Similar Topics

Good afternoon, Guys: we use 1756-L71S and L7SP together, we want to replace 1756-L71S with new L72S, at first we need to assign IP address to...
Replies
5
Views
1,546
We have a Fanuc RJ3 /iB controller. Suspect the CPU is bad. I have a backup of the System files , TP Programs , Application , Applic-TP , Error...
Replies
0
Views
1,805
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
147
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
0
Views
56
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
83
Back
Top Bottom