Powerflex 525 F080 Autotune Failure anomaly?

mylespetro

Member
Join Date
Dec 2015
Location
NS
Posts
740
Hey everyone, ran into a strange issue trying to autotune a motor using a PF525. For context, there's an enclosure with two 525s in it, controlling two motors with identical nameplate data:

575V, 60Hz, 3HP, 3.44A, 1720RPM

We went to run a Static Tune on Motor A through Drive A and we got fault F080 - Autotune failure. After checking the troubleshooting section of the manual, it said either the start command was interrupted or the autotune actually failed. After double checking that we weren't losing our start input (we were jumpering +24VDC from terminal 11 directly to terminal 2 and didn't pull it off), and trying the autotune several times, we kept getting the same fault. Afterwards we ran the Static Tune on Motor B through Drive B and it went off without a hitch. After doing a resistance test of the windings in addition to meggering the motors (11 ohms on all 3 windings on both motors, 550Mohm on the megger on both motors), and thinking about how to narrow down the cause, we swapped the motor leads on the two drives so that Motor A was connected to Drive B and vice versa. We then ran the Static Tune on Motor A (which was failing the autotune) through Drive B and it completed the autotune successfully, while the Static Tune on Motor B through Drive A returned the same F080 fault again. We double checked that the parameters were all the same on both (motor NP data etc), and everything was the same across both. Anyone have any idea why one drive would fail an autotune on multiple motors that another drive were able to successfully autotune? We do have a spare 3HP drive so we're going to try swapping the power section out tomorrow and see if that works, and if not we're going to try swapping out the control module as well. Is it unreasonable to assume that there's an issue with the drive out of the box? The only other thing I can come up with if it's not the drive is some strange wiring issue that is causing an induced voltage in a conductor or something like that.
 
If both motors tune OK through drive B and both motors don't tune through drive A, then I would suspect that drive A has some sort of issue and would need changing, it could be either the power or control module.


Alan.
 
Swapped the power module and it autotuned successfully. Not sure what the issue was, will contact my local AB drive rep and see if he’s seen the issue before.
 

Similar Topics

Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
228
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
233
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
468
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
4
Views
224
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
293
Back
Top Bottom