I don't a lot of experience analog cards. This IFE analog input card has a spare channel I'd like to use. Today I used a 4-20mA signal from a level transmitter into the spare channel. The 4-20mA signal represents 0-100%. When I wired it to the analog in I had to play with the scaling the get the signal to match the digital display from the level transmitter. I had to set the raw scaliing min/max to 0-260 and it worked. Initially I thought I would just set the scaling to 0-100. Any thoughts?
 
Help Anyone?

The 4-20mA signal is provided from a Endress & Hauser FMU 860 level transmitter. Why can't I just set the input scaling to 0-100 for 0-100%?
 
The first tool in your box for this is the User Manual:

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um663_-en-p.pdf

Remember that the 1771-IFE is an ancient but durable design that comes from the PLC-2 days, so it has some quirks left over. The most significant of those is that the scaling factors must be entered in BCD format, even if you are using 2's Complement Binary as the data format. If you are using scaling on one channel, you have to use scaling on all channels and send the full-size 37 word long configuration block.

Are you setting up the scaling in an RSLogix 5 wizard, or manually in the Block Transfer Write data source block?
 

Similar Topics

Hi Guys I'm using Vijeo Designer as HMI, and we're monitoring the water levels in a water well of 6 meters deep. I created the water well in...
Replies
0
Views
1,315
Hello friends; I am new with Mitsubishi system. I need some example to handle the 4-20mA by using FX-2n-4AD which is attached with FX-1N-14M...
Replies
5
Views
3,533
Dear All; Good day. I have a flow meter range 5-70 Cm/hr and out is 4 to 20 mA. first i want to ask how i calculate that at 13 mA what is flow...
Replies
2
Views
1,693
Hi All I am doing a Tank Gauging project. In there all the tank parameter like level , temperature , pressure are coming into a master...
Replies
9
Views
3,867
i'm a newer in PLC programming... anyone please help me about how to do analog scalling in PLC, please sent me an example the ladder for this...
Replies
2
Views
3,282
Back
Top Bottom