Make of plc

Never seen it before but suspect it is a clone of the Mitsubishi FX series there are many versions of them, main differences are limited functionality, 232 rather than 422/485 port.
 
The LEDs all look they show the status of the X (Inputs?) and Y (Outputs?) with nothing to show whether or not a program is running. That suggests the unit is just an I/O device as others have already pointed out. Follow the cable at the lower right. Most likely it leads to the CPU.
 
The LEDs all look they show the status of the X (Inputs?) and Y (Outputs?) with nothing to show whether or not a program is running. That suggests the unit is just an I/O device as others have already pointed out. Follow the cable at the lower right. Most likely it leads to the CPU.

the x and y are seemingly random.... 0-7 10-17, 20-27... but not in order.

30-32.... oops, because we skipped X8,x9, x18,x19, x28,x29 for some reason.... lol


and then they even skipped Y22 for no discernible reason at all... just one random "output" not listed or used, and out of order...

this screams copycat backline 4th shift overnight line running OPS in china.
 
I am betting that the HMI an integrated PLC/HMI, and the part shown in post #1 is an expansion for this PLC/HMI combo.
Search for Samkoon PLC you will find some images of devices that look similar if not identical.
 
This is the rear of a Samkoon PLC/HMI
Samkoon-4-3-inch-HMI-PLC-All-in-one-Integrated-controller-HMI-Touch-Screen-Panel-8DI.jpg_Q90.jpg_.webp

Notice the lettering of the terminals are in the same style.
 
a lot of the samkoon and aliexpress fakes use FX part numbers from real mitsubishi PLCs too. so if you see anything on this that says FX, then I think they're on to something with the samkoon software.
 
plc

no i/o on hmi so not extension, tried samkoon software no joy,hmi configured for modbus coms so no help
 

Similar Topics

Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
0
Views
10
I know this topic has been brought up a few times, but i had some specific questions. I have installed several 1783-NATR devices and they have...
Replies
0
Views
33
Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
31
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
51
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
92
Back
Top Bottom