I am having some issues with a 1794-IE8 flex module on a controllogix plc. this is measuring the weight of a tank on load cells. the scaling seems to be right with the module set for 4-20mA and the raw min/max is 0-30840, but with a measured 3.8mA from the transmitter I am getting a raw value of 40. which is showing the tank as not empty when it really is. we have about 12 tanks set up like this and they all behave the same, and have since being commissioned new. so I am not really going down the road of thinking I have an isolated hardware issue. if I simulate 3.7mA to the module then I finally get a 0 raw value.

any advice on how to tighten this up so that at 4 or 3.9mA I can get a 0 raw?
 
That is 0.1 of 1 %, pretty small error. What is the engineering units (span)?

Can the 4-20ma transmitter be adjusted(calibrated)? If not you could do this in the PLC.

If it is just a high zero issue you could program a zero cut-off. Any thing below value xxx will show zero. Common method as most transmitters drift a little.
 

Similar Topics

Can anyone give me an idea of what the I.Fault and I.Status represent on a 1794-IE8? I can't locate this info in any documentation.
Replies
3
Views
4,252
Hi, i have a configuration whit 1747-SN and 2 racks in flex i/o (1794-ASB). In the rack 1 i have 4 modules 1794-ie8, 3 modules 1794-oe4 and 1...
Replies
1
Views
1,468
Hi, I am back again, still with the issue of getting the 1794-IE8 configured and getting the reading from 1794-IE8. I am using SLC 5/04 series C...
Replies
1
Views
2,319
Hi guys, Recently one of our AB Flex 1794-ie8 Series A analog input module has failed and we replaced it with a new one but a new module is Series...
Replies
8
Views
10,608
New at this so here it goes, Could anybody give me a basic overview of what this type of FLEX I/O does, its an '8 input analog module...
Replies
2
Views
4,822
Back
Top Bottom