Single phase motor wired to 3 phase overload

Marc

Member
Join Date
Jun 2004
Location
Nashua, NH
Posts
430
HI all,

Can anyone explain to me the correct way to wire a single phase 120 volt AC motor to a three phase solid state overload/contactor?

I have seen L1 through contact 1 to the motor with neutral to contact 2 looped back throught contact 3 out to the motor.

I have also seen L1 through contact 1 looped through contact 2 out to the motor and neutral through contact 3 out to the motor.

Also I have seen L1 looped from contact 1 through contact 2 and contact 3 out to the motor with a direct connection to neutral (not through contactor/overload).

Having seen all of these in the field, I am not sure which is correct and why.

Any help would be appreciated.

THX

Marc
 
Hi Dan

Customer requirement.

Besides, I deal with stuff in the field, and have seen all previously mentioned scenarios and am wondering which is correct.

Thanks for the response.

Marc
 
I usually run L1 through contact 1 looped through contact 2 out to the motor and neutral through contact 3 out to the motor. Any f these will work, and I'm not sure there is any advantage of one over the other, although I like to run the neutral through the overload.
 
Tom Jenkins said:
I usually run L1 through contact 1 looped through contact 2 out to the motor and neutral through contact 3 out to the motor. Any f these will work, and I'm not sure there is any advantage of one over the other, although I like to run the neutral through the overload.

Why do you like to run the neutral through the overload? Just curious, because I have not seen that before.
 
The only reason for looping back is if the OL relay is an electronic OL with phase loss sensing. Otherwise, looping back doesn't gain you anything other than extra work. Run L1 through contact 1, N throught contact 3, and be done with it. Contact 2 is not going to get emotional about being left out.
 
OK, easy bit first, we know you have to use all three circuits through the overload otherwise it would trip on single phasing, this applies to both electronic and thermal overloads. If it is an overload directly joined to a contactor then you would want to take the neutral through the combination otherwise the neutral wouldn't be switched which leads to potential danger because Neutrals aren't always at low voltage to earth and I have seen Lines and Neutrals crossed during installation. And my definition of single phase is different to American single phase so that Neutral may not be a Neutral at all. A 230V panel in the UK would be Line to Neutral but if it was moved to the States it may be connected Line to Line for 220V. So I reckon that passing the phase and Neutral through the overload is the smart thing to do. Though either could be used for the second loop through I would go with the Line as, if the Neutral faulted to earth you get greater breaking capacity if the Line goes through the overload twice. So after that meanering ramble I am going for Line looped through twice with the Neutral taking up the third connection.

Bryan
 
Thanks for the replies,


What about the addage that you should never break the neutral? I only ask because someone else mentioned this as a no no and that the line should loop through all three and the neutral should be unswitched.

Not trying to be a pain, just looking for a better understanding.

Marc
 
Marc said:
Thanks for the replies,


What about the addage that you should never break the neutral? I only ask because someone else mentioned this as a no no and that the line should loop through all three and the neutral should be unswitched.

Not trying to be a pain, just looking for a better understanding.
Marc

Breaking the neutral is OK
IF
all conductors are broken simultaneously. Breaking the neut is (was at one time in past ??) required on the circuit breakers supplying gasoline pumps.
The other possibility is where you have a generator isolation (anti parallel) switch. Some utilities may require you to break the neutral to ensure no part of the generator circuitry can connect to their lines.

Dan Bentler
 
Last edited:
Never break the neutral may be a good rule of thumb when neutral is bonded to ground for control circuits.

For motor circuits, you want complete disconnection for a variety of reasons, not the least of which, is that many of your applications for this standard circuit may be 220-240vac single phase motors with a center tapped neutral which is grounded.

You then certainly want to disconnect both motor power legs since one of them is no longer necessarily at ground potential.

I question BrayanG statement about thermal overloads. If only two heaters are warmed below their current trip rating, why would the overload mechanism open? How do thermal/mechanical overload relays detect single phasing?

It has been my belief, (not necessarily fact) that this only holds for a single phasing three phase motor. The overload device will detect it, not because of missing current on one pole, but because of excess current suddenly appearing on the other two.

If all three heaters, (two at the correct load level and one cold one) are happy, and properly matched to the trip current curve of the individual poles, won't it still work correctly?

Help me understand, please.
Thanks.
Paul
 
OkiPC I believe that you are correct. If a 3 phase motor is happily running and then looses a phase or two the remaining windings will rise to the occasion and try to keep up with the load. This increase in current will trip the overload device and disconnect the motor from the line.
 
Loosing one phase may make the other two phases see more current in a three phase system, I think it will depend very much on the load attached to the motor. For instance I would expect the current for a fan to drop on the loss of a phase. One thing I do know is that the thermal overloads in Europe look at the current in each phase and the differential to other phases. I have taken a few to pieces to have a play, they are a bit agricultural when you get inside them with springs and bits of plastic.

Bryan
 
BryanG said:
Loosing one phase may make the other two phases see more current in a three phase system, I think it will depend very much on the load attached to the motor. For instance I would expect the current for a fan to drop on the loss of a phase. One thing I do know is that the thermal overloads in Europe look at the current in each phase and the differential to other phases. I have taken a few to pieces to have a play, they are a bit agricultural when you get inside them with springs and bits of plastic.

Bryan

Loosing one phase WILL make the other two phases see more current in a three phase system

I think it will depend very much on the load attached to the motor. For instance I would expect the current for a fan to INCREASE 3 TO 5 TIMES FULL LOAD CURRENT on the loss of a phase.
As the motor is about to stall.

--------------------------------------------------------------------------




With thermal Bimetal overloads, If a motors Overload is set to the motors full load current setting and loses a phase, a standard 3 phase overload ( as per the brown bar only ) It would trip in about 1 minute, where as if it had a single phase trip capability ( as per the brown and the purple bar ) it would trip in about 15 seconds.

SinglePhaseOverload.JPG
 
Last edited:

Similar Topics

What would happen if you ran a 60Hz Single Phase Motor on 50Hz supply?
Replies
6
Views
468
Hi PLCs.net! I'm working on a multi-motor system, most motors are single phase, driven by servo drives. I wanted to check what kind of motor...
Replies
11
Views
1,463
Any panel I've built with contactors and overloads has been 3 phase. I'm now quoting on one with some small single-phase loads. Definition of...
Replies
24
Views
5,426
Hello everyone, I ran into this 230 single phase two speed motor with two capacitors and a relay (see picture) and have a few questions: The...
Replies
4
Views
1,359
Good Morning , I should know this , but will a 3 Phase overload trip if a 3 Phase motor runs single phase for a long period of time ...
Replies
6
Views
2,123