Siemens S5 135U Peripheral I/O Addressing in OPC Server

shady_yehia

Member
Join Date
Jun 2004
Location
Cairo, Egypt
Posts
30
Hi there.. I'm building a SCADA application with an old Siemens S5 928-135U plc.. i'm using an OPC Server from SoftwareToolBox..

The proplem is that all addresses of the analoge channels of the plc are in the Peripheral I/O area (e.g. TPW128,TPW130) and so on. But the OPC Server doesn't support these addresses. can any body tell me what to do?

Thanks in advance..
 
/agree Andybutcher

Create a "shadow" data block or two, and reference that from your SCADA system.

In the PLC logic, copy all of your Periperal inputs to an "Input Shadow DB (area)", and copy your writes from the SCADA System from an "Output Shadow DB (area)" to the actual output words.

As a general rule, I do that with almost all of our SCADA/PLC systems; that is, never refer directly to any physical I/O area from the SCADA system. I've never considered it a good idea especially to have an external device writing directly to my output tables.
 
Thank You Guys for your help last time.. But another problem just came on the way.

I'm reading all tags very well, but i can't write data to any memory adderess in the data blocks or the flags area. why is that?

remember that i'm using the AS511 Programming port protocol and an OPC server from softwaretoolbox.
 
I am not sure about this as I have only used OPC to read data from a PLC. Are the tags you are reading defined as read/write or are they defined as read only in the OPC server software? This maybe the problem. Another thing, if you establish a new tag and you write to it using the scada, do you see the changing status of the bit or word in the PLC?

Andrew Butcher
 

Similar Topics

Good morning Please i need an advise, I have a s5 135u cpu system , it is installed on printing machine. Nowadays its stop about 10 times in 8...
Replies
27
Views
4,146
I have an Siemens S5 135 system. The CPU 6ES5 928-3UB12 Will not go into run mode even after a MASTER RESET or AN OVERALL RESET using a...
Replies
2
Views
2,837
i have a siemens 135u plc cpu which is in stop mode. the number of the processor is 6es59223ua11. i dont have a programmer so i need help on how...
Replies
8
Views
6,195
hello miss/mr We have a control system that works with plc S5-135U. two cpu (p/n:6ES5 921 & 922)of plc have ram card. The problme is...
Replies
2
Views
1,562
Dear friends I face a problem with my Refinery PLC unit SIEMENS S5 135U -3UA11 is now not functioning The problem start after a CPU's fan fault.I...
Replies
5
Views
8,372
Back