fault on DP s7-414-3 (leds EXTF y BUS2F)

jmrcalin

Member
Join Date
Sep 2005
Location
barcelona
Posts
27
Hello!
I want to configure a Siemens cpu 414-3 as master profibus and a Controllogix SST-PFB-CLX as slave profibus.
I´ve inserted the file gsd (ssti0876.gse) into the hardware S7 to recognize and configure the slave dp, and it was saved and compiled without fault. But when I´ve downloaded this hardware config to the plc s7 414-3, the plc goes in alarm.
The failures are on CPUside the leds EXTF and BUS2F.
Could someone please help to me?
Regards
 
The LEDs say that there is a problem on the Profibus port. So something has gone wrong with the connection to the SST module.

Is the cable conncetion OK ?
Is the SST module setup correctly with the corract station number for example ?
Also look in the Hardware Diagnostics in STEP7 to get more detailed information about the error.
 
Have I configure the slave profibus (SST-PFB-CLX)before than the Master profibus (S7-414-3) ?. Is necessary configure the module SST-PFB-CLX if it only works as slave?
Regards
 

Similar Topics

Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
36
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
3
Views
76
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
90
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
Replies
2
Views
99
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
116
Back
Top Bottom