4-20ma Passive Device Wiring between 2 boxes, with Seperate Power Supplies
I would be concerned about the length of wire with any analog signal
If he does this as 2 wire, loop powered 4-20mA with a single power supply in the receiver panel (the conventional manner), then a 400 foot run is nothing to 4-20mA. Absolutely no signal loss.
I've seen 4-20mA cable runs of over a mile (1.6Km) at the mills that have run for years with no problem at all.
Conventional 4-20mA is VERY robust.
I have no idea if the 2 supply thing will even work, but to me it isn't worth bothering with because loop powered, 2 wire, passive 4-20mA transmitters were designed to work with a remote power supply at the receiver.
2 wire cabling runs from receiver panel to the field is the prime driver for 4-20mA; the wire break fault detection at 0mA is just a side benefit.
+1
Until 300m and if on the same "earth" I don't even think about it as an issue..
If it is another building or longer I'd consider some separators or protection, barriers but 100m is nothing...
And, I'd use the plc power supply too if possible, less possible problems..
It's a bit of a mess before it gets off the ground. Wouldn't some form of remote IO be a better solution.
The OP needs a shielded, twisted pair cable for each transmitter. In my world, that isn't messy, it's conventional and any instrument guy with a DVM can troubleshoot it.
Yes, he could do remote I/O, but for how many signals/transmitters? There's a point where ROI comes into play.
You have analogue signals 100m apart, I would say you've past the point of getting remote IO already, simply on future proofing and trouble shooting grounds alone.
I need to go from a powered 4-20mA output (i.e. transmitter supplies voltage) to an Allen Bradley HART input card 1756-IF16H. I cannot set input...
2,408
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
264
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
269
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,681
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
481