Siemens CPU313C Analog Inputs
sherman4
Jun 2002
46
Hi !
I am new to Siemens S7300 (313C CPU) PLC and I cannot find the documentation related to analog inputs connecting diagrams.
I have a couple of active flow transmitters (4-20 mA) 120Vac powered, which I would like to connect to the PLC AIs, I have connected passive transmitters before to the same inputs (following the diagram on the module cap), but I am afraid that it might not be the same connection type for active 4-20mA transmitters (no 24 Vdc powers the 4-20mA loop).
If anyone does have connecting diagrams available or any web link, please help. I appreciate it.
Thans
[attachment]
In the above example (for channel 2) you would have to connect the 4-20mA signal on pin 9.
If you use channel 0, you will have to connect the 4-20mA signal on pin 3.
Connect ground to pins 4-7-10-13-20. The ground must be looped back to the device that generates the 4-20 mA signal.
Hallo everybody Im pretty new in here about 2 min he he, i would like to get som help setting up my PLC, i have worked with step 7 before but...
3,263
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
20
233
Hi everyone, I am an omron plc tec , lately I came across a siemens s7 200 cn plc . Can someone help me regarding the software required and...
26
465
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
117
Hi, I have PLC S7-1200 and switch XC-208 and Iam trying to implement this SNMP library: SIOS I am not sure, what I am doing wrong, but there is...
122
