Analog inputs module 1769-IF 8, Error Code 16#0010

Elcan

Lifetime Supporting Member
Join Date
Apr 2008
Location
NC
Posts
935
Hi all,
I have a CompactLogix system in the field that had been running without any issues for several months, until one of the 1769-IF8 modules started showing this fault:
"Code 16#0010 Mode or state module does not allow object to perform requested service".
We changed the module position and we even replaced the module with a brand new one, without success.

Any clues?

Thank you!
 
So nobody have had this problem in the past?

I've looked for this error on this forum, and I found this:
http://www.plctalk.net/qanda/showthread.php?t=95647&highlight=Code+16#0010
But it is not related to the 1769-IF8 module.

Also, on the Rockwell website, there are no entries for this error that mention the 1769-IF8 module.

Since the original module itself was replaced, and we've tried with another location in the rack, I'm suspecting the problem is the wiring to the sensors, and I'm evaluating using signal conditioners to fix the issue.

I will appreciate your comments!
 

Similar Topics

I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
Replies
1
Views
142
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
93
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
Replies
8
Views
239
I have a SLC500 5/05 and we have an alarm setup to monitor the status of the Analog Inputs we have wired to a 1746-NI8. We are using 5 of the...
Replies
14
Views
2,774
Hi, I'm curious if anyone has made a master sheet or cheat sheet for all allen bradley card's analog inputs/outputs? As much fun as it is to...
Replies
2
Views
1,564
Back
Top Bottom