Panelview 800 INT to Floating point

Join Date
Dec 2017
Location
Romeoville
Posts
3
Hello All,

Panelview 800 and Micro1400.

Getting Numeric entry to read an INT from PLC, but display as Floating point.

EX. INT in PLC N7:20 == 85

I'd like Panelview800 to read that value as 8.5. If user changes value to 8.7, INT in PLC should read 87.

I can't seem to get the HMI to do this. I've got my num entry properties set to 1 decimal position, tag is configured as 16 bit int. Numeric field width is 4, as largest value I want to see is 999, or 99.9 on PV800.

Does anyone have any suggestions as to what I could be doing wrong?

Thank you!
 
Wanted to add that I can get the value to display instead of 50 as 5.0 using tag scaling in Panelview800. However, if I type 5.4, it rounds it back down to 5. If I type 5.6, it rounds up to 6.

The PLC sees this as 50 and 60. I want to to see 54 and 56, respectively. How do I stop this rounding?

tagSetup.JPG Properties.JPG
 
You could always use a floating point number in the PLC, tie that to a tag on the Panelview 800 so it displays properly then in the PLC just convert that floating point number into an integer. At least that’s what I have in my head.
 
I've gotten rusty on my PanelView software, and I've learned so many HMI packages over the years that I get confused over which software has which feature.

It's not clear as to whether you are trying do this in the tag database or on a direct link on the graphic. But I believe that you can edit you link to be something like:

( [PLCtopic]::N7:20 ) /10.0

doing the math in the link itself. I also have a memory fragment that says that sometimes putting in '10.0' instead of '10' helps the software know that the result will be a real, which it wouldn't expect considering that the source is an integer. Not sure which package that memory is from, just remember that it worked somewhere in my career.

Tag databases (not necessarily in PV) sometimes have the ability to scale PLC values, back when PLCs did everything in 8-bit math, and the HMI handled the engineering unit translation.

I think I've been doing this stuff for too long....

HTH
 
Hello All,

Thanks for the replies.

To clarify, I am trying to get this done in the HMI itself.

I do not have access the the PLC program.

What I do have, is a N7:20 variable that represents a tank level, changing from 0 to 346. This number actually equates to 0 to 34.6. I need my panelview 800 to show this.

My tag configuration was posted above, so you can see the scaling in there. The panelview is taking the number and scaling it down correctly. If the value in the n register is 150, the panelview shows 15. However, if the n register is equal to 154, instead of showing 15.4, the panelview shows 15. The panelview is rounding the value down if below .5, and up if above .5. A PLC value of 156 displays as 16 on the panelview 800.


Since posting, I've contacted AB tech support for assistance, and they are currently investigating.
 
Try and change the tag that you have in CCW that is attached to N7:20 to REAL instead of 16 Bit Unsigned Integer.
 

Similar Topics

As the title says, I'm using CCW with a PV800 (and Micro850). I've made a scheduler in which a user can choose a month, day (1-31), hour (0-23)...
Replies
15
Views
452
Hello, So i managed to read the string coming from control logix and put a string display in PanelView 800. Now I am struggling to do the other...
Replies
1
Views
115
Good morning all, programming a Panelview 800, I have a maintained push button programmed on screen 1. I copied and pasted it to screen 2. Could...
Replies
2
Views
1,138
I'm trying to convert an old panelview 600 application to the 800 and I'd like to keep the current serial comms configuration instead of adding...
Replies
1
Views
559
Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
Replies
5
Views
871
Back