AB Micro 1400 TCP MODBUS Issue
Kal_H
Dec 2016
ND
I'm working with an AB Micrologix 1400 series B communicating with a Banner camera via MODBUS over TCP. I was able to get everything setup and communicating great, no issues. Until I cycled power, after I did a power cycle my MSG commands errored out with a communication timeout. After a lot of poking around, I finally unplugged the Ethernet cable from the PLC and plugged it back in. All of the sudden the communication started worked again. I forgot to mention I have the camera connected directly to the PLC, no switch or anything else in between. I have done a lot of experimenting and I found that every time I cycle power I wait 2 minutes and then unplug and plug this cable back in and it works. There is no power up sequence between the camera and PLC that changes this, and nothing I can do in the PLC code to change this. Has anyone else ever seen this behavior before? It is the craziest thing I have ever seen. Does anyone know what unplugging this cable from the processor would affect?
When you power cycle, is it just power cycling the PLC or is it power cycling both the camera and the PLC?
If it's just the PLC, my wild guess is that the camera is somehow not resetting its TCP socket connection when the PLC power cycles.
If you have a dumb hub or a managed switch that can port mirror, I'd use that to perform some Wireshark sniffing to see what the TCP traffic is like between the PLC and the camera. It should give you some much-needed diagnostic info to narrow down the possible causes.
Thanks for the response. I'm power cycling both devices, the entire panel to be exact. I'll check into that.
Are you using the ML as TCP master or slave? I've had issues with the ML1400 as TCP slave, if you try to poll it too fast it will eventually timeout every single time. I had to slow the polling rate down to once/second to prevent it from eventually timing out.
The ML is a TCP master, it polls the camera for information. They system works great once I get past my startup issue. I forgot to mention I do have feedback from the camera. As soon as the system powers up there is a a network light that is lit on the camera. It is lit like it sees the network but does not flash with network traffic. Also there is a TCP status page on the camera that says connected. I really think the camera is doing everything right. I think it's the PLC that's not, maybe it's waiting for the camera to renew it's socket connection? I think if I could re-initialize my TCP port on the ML everything would work. Is there any commamd for something like that?
It does sound a bit like a timeout issue on the TCP layer of the comms.
If you want to narrow your investigation down to the MicroLogix side of things, you can test it out by connecting the MicroLogix to your laptop and using a slave simulator to replicate the camera.
For example, see if the MicroLogix is able to maintain Modbus comms when you stop then restart the TCP session on your simulator. Also, you can easily run Wireshark alongside the simulator to see the packets being sent out by the PLC - just to make sure everything is as you expect it to be.
SOLVED!! - I added an unmanaged switch between the devices and that solved the issue. I'm going to try a cross over cable yet to see if I can get away from using the switch, but it is solved. Thanks to everyone that contributed.
Hi! Last few I've been trying to send message from MicroLogix 1400 to Micro 850. Unfortunately every time I failed :banghead:. Did someone tried...
3,177
Hello, There was a mix up in information on some redeployed equipment and two of the micro 1400's that came in were hooked to 120v when they...
1,947
I am trying to exchange data (N registers) to and from a Control Logix PLC. I am programming the messages in the Control Logix program, to...
2,147
Does the 1100 only have 1 high speed counter, but it can have multiple inputs? And so then the 1400 has 6 HSC and you have a choice of multiple...
1,714
Error: "Program in processor has changed causing offline state. Do you want to upload?" RSLogix500 V8.10 Micrologix 1400 Customer wants to add...
2,263