Program in auxiliary PLC
mylespetro
Dec 2015
NS
740
Hey everyone,
Just wanted to see if anyone had any opinions on programming in a PLC that is essentially just being used to store data that's being written to it by another PLC? We have a lift station with a CompactLogix doing the control, but the spec called for a serial radio link back to the water utility, therefore the panel builder put in a MicroLogix 1100 to interface between the CompactLogix and the radio. I have all of the digital and analog I/O being written into the Micro from the Compact and have the I/O labelled, but what would you consider the bare minimum programming (if any) inside the Micro if it's not actually controlling anything? Would you include a comms heartbeat? Or something more elaborate?
Thanks in advance!
Heartbeat - Yes.
As far as other things, I like to put logs in for runtime, pieces count, cycles, etc. Just so next time I get to it I can tell the customer things like "this pump has run 12 thousand hours", "this machine has produced 128 million parts" and other numbers they, and I, am usually impressed with.
I don't know why you would need an interface PLC unless the radio is serial and the compactlogix is not. I would use a heartbeat yes.
The radio spec'd by the panel builder was serial only, but what arrived onsite has a digital/Ethernet jack so it may have been unnecessary to use the MicroLogix after all.
i would have to rethink the idea of using a PLC to log data they are really not designed for that. They would have limited storage at best.
i would look a computer with real hard drive and maybe even look at writing to a cloud drive it shouldn't be to hard to setup.
From what I interpret from this thread, I don't think it's logging data so much as just acting as a data buffer and serial to Ethernet converter between the Compactlogix and the serial radio network.
Just because the radio has an Ethernet port doesn't mean the network supports it.
For example I have a network with MDS SD4 radios mostly but they are all in transparent or 710a mode as some of the radios are MDS 4710. Due to that I cannot use packet with Mac which is the mode that supports Ethernet. I use that port just for the web interface to configure it when on site. That is it.
On a side note. 400mhz is very low bandwidth for Ethernet comms. 900 and above is better but the higher the frequency the shorter the distance and the better the path needs to be (no trees in the way) 400mhz will cut through trees.
I prefer to do modbus when switching to serial comms for the radio network.
Hi. I have a 222 CPU. I need to recover the program from the eeprom memory. Is it possible?
78
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
82
158
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
122