I just replaced this drive as the old one went out when the plant had a power surge/flicker.

1-Installed the drive
2-Powered up
3- Got an immediate EARTH FAULT, so I check the manual and it talks about wires being grounded.
4- Disconnected wires from the motor and ohm out the wires to ground( CHECKS GOOD)
5-So I ohmed out the motor and I was getting 40-50 ohms when tested to ground.

6-I have not powered up the drive with out the wires disconnected. I will try that next to confirm my thoughts that the motor windings are starting to go bad and current is leaking out.

Bad motor?
 
Yes. Less than 10kohms is failing. Some drives require much more than that to overcome a ground fault.
šŸ™ƒ
That should read 10 megohms. I have seen motors on starters work as low as 2 Mohm. I once replaced an obsolete 1336 VFD with a Toshiba G7 and it wouldn't run. The motor megger test showed 80 Megohms to ground... The 1336 was fine with it, the G7 said nope.
 

Similar Topics

Hey all. I tried to startup a drive last thing before leaving for the weekend. On power up, the drive constantly gies earth fault. This is with...
Replies
8
Views
2,163
Hi Team, I am working on one Paper Coating machine, My Winder, infeed, Coater and Unwinder is runnning through ABB's ACS550 VFD, My winder is...
Replies
0
Views
1,287
Iam getting Fault F021 ("System Fault Current Measurement is out of range"),Any help ??
Replies
1
Views
2,954
Please i need help i lost all setup parameters to control 3 pumps pressure i put again some of them but i get stuck in ref 1,2 choice and...
Replies
2
Views
1,417
I am having problems connecting my L32E to an ABB ACS550 RETA-01 Ethernet/IP Module. AB tells me the problem is with the RETA and ABB tells me it...
Replies
9
Views
2,336
Back
Top Bottom