Memory Reset not working Siemens PLC
uptown47
Feb 2008
Over there, next to those boxes
1,146
Hi all,
Correct me if I'm wrong but if I hold down the MRES switch on a Siemens 300 series PLC and wait until the amber light stops flashing, then release the switch and hold it down again quickly (causing the amber light to blink rapidly) then this should reset the memory?
This doesn't seem to be working on two different 313C PLC's. I do an "overall reset" but when I interrogate the PLC the program blocks (eg. FC1, FC2 etc) are still in there?
Does the overall reset not clear these out or are they held somewhere that's not being erased?
How do I quickly erase these blocks?
Many thanks
The memory reset does not clear blocks that are located on the MMC card. It only clears the plc and the blocks are then loaded back to plc. If you have a Siemens FieldPG or an external Siemens prommer you can erase the card offline in Step 7. Another way is to use image files and tools from this site then you can use any card reader. Search for MMC on this forum and you will get more help.
You can go online in step 7 and select the blocks you want to delete but not all attributes are deleted this way. To delete all the only way is an external reader.
You can clear all data from an MMC card like this:
Instructions:
It is not possible for users to format an MMC. All you can do is "reset" an MMC, which deletes all user data. Proceed as follows.
  1. The MMC is slotted in the bay of the CPU. Your CPU requests an overall reset (slow blinking of the STOP LED).
  2. Set the switch to MRES and hold it there (approx. 9 seconds) until the STOP LED lights continuously.
  3. Within the next 3 seconds you must let the switch go and set it again to MRES. The STOP LED now blinks during the delete procedure.
If the MMC continues to request an overall reset after the procedure described above, then it is defective. Note:
It is only possible to reset the MMC if it contains data that is invalid for the CPU. Otherwise the MMC is only initialized by the procedure described.
JohnW said:
Note:
But then you need to put your mmc in another diffrent cpu or? Do you know if this procedure deletes the Saftey attribute for F-Cpus aswell?
That would confirm my experiments... 2 PLC's, if I swap the MMC's then they request a reset (ie. blink the amber light). When I do the reset it clears the MMC completely.
However, doing a reset to an MMC that has the correct PLC info on doesn't clear any of the blocks..
So, it seems the only way to clear an MMC is to do it online via Simatic Manager.
Thanks for all your help. Much appreciated.
(y)
my s7 313c is stop led flashing evry time and i there is no connection between the plc and pc is the diffrent version is effecting and i made rest memory by mrs and main but is not going well flashing stop led
hello Friend There is one old system with S7 300 CPU which is password protected and I dont know the password. Now I want to remove the password...
5,904
Hi. We have one machine which has 90-30 plc. Because of the some unusual alarm messages, machine manufacturer recommend cpu ram memory reset. How...
4,009
Hi. I have some (quite basic, actually) questions: 1) Does anyone know exactly what happens when you perform a Memory Reset on a Siemens S7300...
1,431
This example describes various possibilities for presetting memory areas with certain values for clearing defined memory areas. The...
2,615
Hi to All, Actually i am looking on how to reset/delete the memory in the A-B L32E COMPACTLOGIX CPU? as like in SLC to reset memory we have to...