SLC 5/03 indirect addressing error
technolog
May 2015
Ohio
316
I'm trying to set up a 1746-HSCE2 high speed counter module in a SLC500 with a SLC 5/03 processor. The manual - http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um002_-en-p.pdf - gives an application example on page 6-7 using indirect addressing. However, when I try to verify the project, I get an error saying "Indirect addressing is not supported on the current processor type for the N file type".
The manual states that indirect addressing will only work with SLC 5/03 and higher processors. I have an SLC 5/03. The example in the manual also uses the N file type, so I don't know what the problem is.
The offending instruction is
COP
Source #N12:[N13:0]
Dest #O:5.0
Length 8
If anyone could offer any insight, it would be very much appreciated.
Using Indirect Word Addresses
You have the option of using indirect word-level and bit-level addresses for
instructions specifying word addresses when using an SLC 5/03 (OS302), SLC
5/04 (OS401), or SLC 5/05 processors.
The operating sytem needs to be OS302 or higher, yours is?
OS301 :)
I went ahead and did the programming using direct addressing and have both encoders counting, I'm very pleased to report. Out of interest though, is it possible to change the OS and if so, how?
I recently did a conversion from an SLC to a CompactLogix and I am having trouble with a specific piece of code where the SLC used indirect...
2,840
I would appreciate some help understanding some code from the RSLogix 500 days. I'm trying to convert a Studio and I get a PCE for the following...
2,248
tough one to get my head around but here goes: N27 is a file that stores whether the recipe stored was valid. N12 is a file that holds recipe...
1,541
I have a whole bunch of analog inputs that I need to scale to process values. Using JMP and LBL can I use indirect addressing to cycle through all...
6,142
Hi All, AB SLC 5/03 What are your thoughts on "repetitive identical sections of code"? Would you write it once and indirect address the...
44
15,396