fault on DP s7-414-3 (leds EXTF y BUS2F)

jmrcalin

Member
Join Date
Sep 2005
Location
barcelona
Posts
27
Hello!
I want to configure a Siemens cpu 414-3 as master profibus and a Controllogix SST-PFB-CLX as slave profibus.
I´ve inserted the file gsd (ssti0876.gse) into the hardware S7 to recognize and configure the slave dp, and it was saved and compiled without fault. But when I´ve downloaded this hardware config to the plc s7 414-3, the plc goes in alarm.
The failures are on CPUside the leds EXTF and BUS2F.
Could someone please help to me?
Regards
 
The LEDs say that there is a problem on the Profibus port. So something has gone wrong with the connection to the SST module.

Is the cable conncetion OK ?
Is the SST module setup correctly with the corract station number for example ?
Also look in the Hardware Diagnostics in STEP7 to get more detailed information about the error.
 
Have I configure the slave profibus (SST-PFB-CLX)before than the Master profibus (S7-414-3) ?. Is necessary configure the module SST-PFB-CLX if it only works as slave?
Regards
 

Similar Topics

Any one give solution for this fault. We are using AB Gaurd logix controller(5573s), resent days we are facing major fault in controller...
Replies
1
Views
66
I migrated to a WSP2023 application. Now when I open a HMI object (for example a valve or motor) the popup is first correctly show as defined ...
Replies
0
Views
35
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
115
Good morning everyone I’m currently working on a omron device net and have a nord drive that fell off the network. I have limit knowledge in...
Replies
3
Views
139
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
90
Back
Top Bottom