ATEX Intrisic Safety (IS) question.
DLMUK
Jun 2013
Southampton
311
I have an application which is in an ATEX hazardous area, the instrument being used is lower power and qualifies as 'simple apparatus' and is connected from the safe area via an IS barrier.
The setup is:
Instrument -> cable -> barrier -> safe zone
What I would like to know is, if we put a connector on the cable half way down its length, but within the hazardous area, does it require and ATEX approval?
As the power is limited by the barrier before the connector, I can see an argument that the connector type doesn't matter. I have also seen applications where both ATEX and non ATEX connectors are used.
thanks
What type of connector? Just terminals?
Are you altering the characteristics of the loop? E.g adding any capacitance/impedance?
I'd be wary with calling items 'simple apparatus' unless certified as such by the manufacturer. To certify yourself you need to prove it meets around 7 BS EN Standards. Some of which needs lab testing to verify.
@Rob
thanks for the reply. The item has already been confirmed as Simple Apparatus by an authorized UK test house.
What we want to do is just add a connector to help with installation and maintenance. So that the instrument can be easily removed for calibration. It would therefore be an inline cable end connector, one male and female receptacle.
We haven't specified a connector as unsure what is required at present. Something along these lines would be good:
https://uk.rs-online.com/web/p/mil-spec-circular-connectors/2982409/
thanks
I would think that as it has been passed through a barrier you're ok using something like that. I'll have to check though.
Regulations will most likely stipulate that it can't be plugged or unplugged whilst the circuit is energized.
You will still require that the plug conforms to the IP rating for that particular area (or perhaps it's fixed for IP65).
And the distances to the 3mm to earth and 6 between different loops.
Most likely and to err on the side of caution, anything Exe will do. I would also try to find a connector with an end cap to protect the terminals if the sensor is to be removed and not replaced. I don't think it is required, but can protect you concerning the condition of the loop.
I would also have a quick look on the rating for dust as the conditions compared to gas and vapours are different.
As stated by Rob there shouldn't be a problem as long as you don't add impedance or capacitance to the circuit, which you don't if the connector is just that. The connector doesn't need to be Atex approved since it's part of the IS loop. Just make sure you document it in you IS system description for that circuit.
DLMUK,
if by connector, you are referring to terminal block, it depends on the environment.
if by connector you mean a micro connector, it still depends on the environment.
what ever the environment, you must use a seal off within 18" of the safe zone. the seal off being in the hazardous area. Rigid pipe, myers hubs, and conductive sealant ( not sure on this in the UK) as well.
the terminal block or connector must also meet certain criteria. I do not know the current UK rules, so please check.
cheers,
james
Hi - I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing...
940
I`m searching for a remote mobil panel (battery driven), for controlling some IO on a PLC. The remote mobile panel need to be approved for Atex...
2,064
Hi all, i have to connect a panel that is located in an atex area. The patchcord that connects this panel to an outside switch should be a normal...
1,733
Hi all, Does anyone know of an ATEX 2/22 sensor that I can use to measure and control the edge of a belt? The belt is metal and could get a...
1,152
Hello Do any of you know of a PLC with an Atex Zone 1 approval? Does this exist? We have an application on a piece of mobile equipment where we...
2,328