DC power meter with analog output
Nov 2011
Ireland
182
Hello
i need a DC power meter that gives a 0 - 10V along ouput signal. i need this signal for a plc.
the power level to be measured will be small i.e. pobolaly less than 10 Watts.
so i need a small cheap DC watt meter or some other way of measuring power. unfortuatley i only have one analog input available in my PLC
can anyone tell me where i could buy one?
thanks
can you refference your plc 0v and load 0v ? if so, you could just put a serial resistor that would give a differential voltage at full load. According to load voltage, maybe not use full span to obtain 10v as it will remove 10v out from the load too...
te voltage is very easy just 2 resistors to make the 24 voltage max 10.
possible with resistor of 10 kiloohm and one of 15 kiloohm.
the current is possible with a current converter (look at arduino for a cheap one.acs758
to have both analog inputs use a relais switching between both inputs (you will need another output for this.
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
305
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
64
I have several Siemens 9410 power meters throughout the factory. What is the best way to connect them to Control Logix PLC? Thanks.
1,313
Hi All, I am using an Accuenergy Data Acquisition Server (https://www.accuenergy.com/products/aculink-810-data-acquisition-gateway-server/) to...
2,676
Hi, I am kinda newbie here. Actually, Can I take the Power data from PM5330 Schneider Electric (KWH,Voltage,Ampere) to my Allan Bradley Micro 850...
1,623
