Net-aic compatibility with micrologix 1400

Join Date
Sep 2017
Location
Mumbai
Posts
28
Hello frnds....

i configured channel 0(8-pin port) of my Micrologix 1400 PLC to DH485 & download Program in PLC using Ethernet.

& now i want to communicate my PLC to PC through NET- AIC using same channel i.e channel 0(8-pin).
is it possible???????


reply for suggestions....


Thanks and regards
Rutesh deshmukh
 
How are you connecting to your PC?

You may need additional hardware. Answer the above and someone can help if necessary.
 
8-pin of NET-AIC is connected to channel 0 of PLC and 9-pin of NET-AIC is connected to the PC . Also i configured channel 0 of plc as DH485 driver. is it possible to connect????
 
The 8 pin mini DIN is RS232 only on the AIC. If you configure channel 0 for RS485 then you need to use a 1763-NC01 to connect to the RS485 port on the AIC.

Why not just connect Channel 2 on the PLC directly to the PC?
 
thanks for your reply....

Actually in my old system i installed micrologix1500 & now i replaced 1500 with Mocrologix1400 .that's why m try to use channel 0.


is it possible to connect channel 2 as it is DH485 to PC or should i need to connect
NET-AIC?????
 
I think it best if you describe what is currently connected to each port and what it needs to do.

If you were going to connect directly to a PC with channel 2 it would need to be set to DF1 full duplex.

What application are you running on the PC?
 

Similar Topics

Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
Replies
13
Views
1,750
I've attached pics, below. I'm in the field right now an am trying to communicate to the Micrologix 1500 through the 1761-NET-AIC (Ugh!) to...
Replies
6
Views
1,908
The manual for the 1761-NET-AIC shows connecting a PC to DH485 network with a 1761-PM-02 cable. Is this done using a DF1 driver set to...
Replies
0
Views
1,048
A customer of mine has a ML 1500 LRP connected to a Net-AIC+ via the mini din connector (CH 0 of plc to port 2 of AIC) from this AIC then connects...
Replies
3
Views
1,753
I have a bunch of ML1000 PLCs on a DH485 network using 1761-NET-AIC modules and we are replacing the ML1000s with ML1400s. Once all of the...
Replies
3
Views
1,962
Back
Top Bottom