I'm having a little problem configuring my WinCC project.

I have a Profibus network with 1 master and 8 slaves (each PLC with alarm_S data), now I can get the master PLC connected to the WinCC but the slaves won't connect.
When I compile the OS it says that I havn't configured a network connection for the slave PLC's, but they already communicate with the master, so the network is fine.

Any ideas on how to get this fixed?
 
If I've understood correctly, you have 9 PLCs all linked by Profibus with one configured as DP master and the others as DP slaves.

In WinCC you need to define a connection to each PLC individually - I think this will require a Full Softnet licence rather than the Softnet Lean licence that comes with WinCC 7.

Alternatively you can pass data between your Master and the Slaves and then have the SCADA communicate only with the Master or put them all on Ethernet - much simpler.

Nick
 
Yep, that's my setup.

I'll have to look for the Simatic net DVD them. Hope someone here has one (bit early now, nobody's here yet but me)

Ethernet is for the following project (this is type installation and I'm not allowed to change many things at once)

Copying evertyhing to the master (and use it as a data concentrator) is not what I want because every cel has it's own plc and sometimes we have 2 cells but sometimes 20 and want it to be as flexible as possible.
That's why the alarms (alarm_s) are in the slaves.

Thx for the help.
 
OK, got the DVD and installed it.

How do I configure the connection, because I can't see option for it in the Netpro.

This is a screenshot of my problem:
No_connection.jpg


as you can see, the master is connected, the rest isn't
 

Similar Topics

Hello, I'm Alex from Spain (sorry for my bad english). Firstly, I'm a newbie at Siemens PLCs and HMI, I have been reading this forum for hours...
Replies
2
Views
1,570
I'm trying to connect Wincc Flexible 2008 Advanced into SQL Server 2005 via script. For the test I made a db in the SQL as db_kalup and created a...
Replies
1
Views
7,220
Hi, i am beginner with WinCC and i need help, i connected the Temperature transmitter with a SM331 module on PLC so i can read a temperature value...
Replies
8
Views
4,060
I am upgrading an old version wincc to V7. I want to use AS511 communication. Can I communicate 2 S5-135u cpu's to my WINCC SCADA runtime using...
Replies
0
Views
2,003
Hi Guys! I have two S7-300 PLCs which are redundant using Siemens Software Redundancy and I need to monitor the data of those PLCs in one HMI...
Replies
2
Views
2,158
Back
Top Bottom