PV600 comm problem
RickParrot
Nov 2015
Iowa
68
I have a PV 600 (2711-T6C16L1, Ser-B Rev-C, FRN- 4.43) It has a RS 232 port I believed is used for printing, and a RS 232 DF1 port.
I am trying to RS Linx with it using an NC 13 cable on the DF1 port. No luck! Help? I would like to wipe any old program out of it and use it wherever it would help.
The RS232 port is probably set up for DH484 get your 1747-UIC out and put a serial cable on it, dont forget to move the switch. auto config will not work, set linx up Device: 1770-KF3/1747-KE Baud: 115200 Parity: Even Error Checking: CRC Stop Bits: 1 Protocol: Full Duplex and whatever your computer is seeing the UIC for a comm port
How are technicians/ engineers supposed to know all that. My odds are better winning the Powerball than to stumble on the settings you gifted to me. I will try them. Don't know if I have a 1747-UIC.
The part number 2711-T6C16L1 tells us that the communication serial port (not the printer port) is set for DF1 Full Duplex communications. That's the port labled "RS-232 DF1".
It is definitely not DH485. A 1747-UIC will not work with it.
PanelView Standard terminals use a "DCE" type serial port. To connect it to a PC, you need a "straight through" serial cable.
The common 1747-CP3 serial cables for SLC-500 controllers are null-modem type, not straight-through.
The 2711-NC13 cable is a straight-through serial cable, or you can use any off-the shelf cable that has pins 2, 3, and 5 one end connected straight through to pins 2, 3, and 5 on the other end.
The default settings for a DF1 Full Duplex driver in RSLinx Classic should work with the PanelView Standard. Delete your driver and start from scratch with a new driver instance.
Are you using a USB/RS232 converter ? Some of those are lousy and many of them won't work with the Autoconfigure feature, which is why I always recommend simply creating a new driver instance and using the default settings.
Ken, Thank you for saving me the purchase of the UIC. I am not using a USB/RS232 converter. My programming laptop was ordered with a serial port. I do have the 2711-NC13 equivilent. I made it myself and tested the pin out. Ill wipe the DF1 driver and start again.
Wiped all drivers, closed Linx and reopened. Com1, , SLC/ Micro/ Panelview, Starting baud rate, 19200, station number 00, parity, none, Error Checking, CRC, Stop bits- 1, Full Duplex.... Auto Config and ...... NOTHING! Time to go home!
Double check your cable (straight thru)
Pin 2 to 2
Pin 3 to 3
Pin 5 to 5
Default settings for your PV is.. See pdf
Just off the top of my head I believe it is the "Printer" connection that you need to connect to in order to program the PV600. You need to get into the settings and change the printer to disabled. After that the panelbuilder 32 software should be able to communicate.
FYI, you can use both if the printer is disabled. (either/or)
Just set up a test app with a PV600. Validated with no errors. Comm protocol DHH485. Just because part number lists it as a 232 port does not mean that the terminal cannot be configured as 485.
You can't just configure a DF1 Standard PanelView for DH485, it would take a hardware change and probably firmware.
I have several machines running 485 out of the 232 port. Not using a blue hose either. The only way to talk to them is 485 with a UIC
Thats true, but you cannot just reconfigure a standard PanelView's DF1 RS232 port to DH485 with a software (PanelBuilder32) configuration.
I am trying to program a stubborn PV600 and having comm problems. Once source says I need a 2711-NC13 cable with just 2-2,3-3, and 5-5. Another...
1,211
Good Evening Everyone, I have a PanelView standard 600 touch only 2711-T6C2L1X(DH485) and I have a 600 T6C20L1(Ethernet). Is it possible to take...
1,918
Hello experts, There's an existing PanelView600 (2711-K6C5 which has only RS-232-DH485 communication port) communicating to a MicroLogix 1500 (it...
35
15,387
Hi All, We have a PanelView 600 -- 2711-B6C2, USB to DH485 converter -- 1747-UIC, and DH cable -- 1747-C13. I've installed the drivers for the...
3,248
I'm a beginner to PLC and Hmi programming. any one please help how to connect HMI to pc. HMI has a printer **** enabled by default, It does not...
424