Wrong analog input readings
showshocka
Mar 2011
USA
510
Hi. OK, i have a pressure transducer for a run tank level (h20 based) that i just checked for accuracy. it's reading 3.999ma at .001in.of h20, so that's correct for an empty tank. my problem is that the way they have it wired is a signal loop................ A + and - voltage from a dc power supply is going to a PLC 5/8OE analog input card which one wire goes to the transducer to the + terminal, the transducer - terminal goes to the + analog input card on the SLC 5/04. From the SLC 5/04 analog input - terminal goes back to the pressure transducer and is wire nutted to the negative wire that goes back to the PLC 5. analog input card.The biggest question i have is that when the tank is empty the SLC 500 output the the operators panel reads 53LBS and the output from the PLC5 to another operators panel reads 285LBS. i'm thinking it must be the math functions in each of the PLC's. I have a funky little drawing for you guys to laugh at, i'm sure someone will direct me to a program i can use for creating such illustrations.
What is the scale from your plc5 to your transducer, and what is your scale from transducer to slc 500. What kind of transducer is that ?? Take a picture of both plcs configs. Take ( voltage/current) measurement at both input/output at the transducer when minimal value is sent from plc5. That will help you with scales.
If that is a 4-20mA current loop its wired wrong at the SLC500.
From the transmitter + to the PLC5 +.
From the PLC5 - to the SLC500 +.
From the SLC500 - to the transmitter -
Wired the way it is, I am amazed it works at all.
Perhaps you could post a link to the Data Sheet/Manual for the Transducer.
This might be a good application for a 4-20mA splitter.
Stu....
Where's the loop power supply in the diagram?
Does either PLC provide loop power at its AI terminals? ? ?
it's a Rosemount 1199 diapram series....the tank is not empty any more but when the tank was empty i got a reading at the transducer of 3.9ma at .001h2o level.
PLC5shot.jpg SLC 5_05shot.jpg 287354_243268765693665_100000316296453_770185_2654407_o.jpg
Your PLC5 Screen Shot appears to be a Simulation Routine, not live Data.
Stu....
As others have stated, it does not appear that things are wired correctly. Also some of the older PLC 5 analog in cards have dip switch settings to configure an input for either a voltage or current input as well as setting the range. And then there is some configuring that has to be done using a BTW instruction as well. It can be a pain in the !!!
Maybe the problem would be easier to conquer if you cut down in size. First concentrate on getting the transmitter to work with just the slc, then once you get that working, put the plc 5 into the loop.
Go to AB's website and get the info for each analog card. There will be examples on how to wire them for 4-20ma inputs.
Just hang in there, work through it and you will have learned a lot.
correction, after further in investigation. this is the final wire chase. still the same the operators readouts are off PLC's are still off.
nope, that was live data as we are running now. why did you think that? the panel-view was showing 4020lbs.
Because the Subroutine is called Simulation, and the Add Instruction is preceded by Simulation Timer #9, and you don't usually use an Add Instruction for Scaling an Analog Signal.
Stu....
Hi all I am having a very weird problem with my control system. I have flex I/O communicating via control net to a RS5000 processor. The analog...
5,725
Hello all, after finishing throwing rotten tomatoes at the screen :D please help me 🤞🏻 . I have a MOSCAD system from Motorola which...
4,152
I am latching and unlatching "result_Data_latch" bit within same rung. Will This copy/move instruction execute correctly??
177
We have a quad monitor setup with FT SE and we are utilizing a header screen at the top of every display. when we open a new page we abort the...
88
Hi all, I am having an issue with FT View Studio ME when I try to open the propoerties of any object, the size of it is very big and doesn't let...
101