RSLogix 1756-L71 Read Only Tamperproof Tags

delforum

Member
Join Date
Jul 2014
Location
US
Posts
7
Hello PLCTalk Experts,

I am looking for an elegant solution to allow viewing of the tags current real values in the database by an unauthorized user, but also prevents the other RSLogix user from ever changing the array of real numbers in that tag.
Do you have any suggestions on how to setup the ladder or AOI using source protection to lock the routine?
 
I can understand why you would want to keep maintenance from making program changes, but WHY would you want to keep another programmer from making changes?

my coworker trust each other and we make changes all the time.
we discuss the program changes the next morning.

please explain your application in more detail.

regards,
james
 
Hello PLCTalk Experts,

I am looking for an elegant solution to allow viewing of the tags current real values in the database by an unauthorized user, but also prevents the other RSLogix user from ever changing the array of real numbers in that tag.
Do you have any suggestions on how to setup the ladder or AOI using source protection to lock the routine?

Why not just write a constant value to a tag? This stops any changing of values during runtime or choose the 'constant' propery in the Controller Tags?


Regards

Daniel
 
Safety of the equipment is the main concern. If those tags change the equipment could be damaged by higher than rated pressures. Adjustments need to be made but infrequently and only by trained service.

With the constant property marked, what steps would be needed to change the register value? Can it be changed while in remote run online?
 
Safety of the equipment is the main concern. If those tags change the equipment could be damaged by higher than rated pressures. Adjustments need to be made but infrequently and only by trained service.

With the constant property marked, what steps would be needed to change the register value? Can it be changed while in remote run online?

I believe the constant tag value has to be amended offline and downloaded complete but im not 100% sure on this.


Regards

Daniel
 
Safety of the equipment is the main concern. If those tags change the equipment could be damaged by higher than rated pressures. Adjustments need to be made but infrequently and only by trained service.

With the constant property marked, what steps would be needed to change the register value? Can it be changed while in remote run online?

Hi Delform.

I have checked this for you on Emulate 5000, so the constant is declared via a Constant 'checkbox' in the Controller Tags and the value can be freely ammended offline/ online using the monitor tags window.

If an attempt is made to write to a constant tag through a routine; a compiler error is generated, so basically the value can only be updated directly.


Regards

Daniel
 
If it's that important, hard code the values in a move instruction in a protected routine. Only give the source key to the ones that you want to change. Anyone can still view in the tag database.
 
Thank you Daniel, James and Phrog for your insights. The constant tag may work well if I can put it in a protected AOI local tag database. Then in authorized persons couldn't change that tag value. How would I get that value from an AOI tag into my main task's routine?

Putting move instructions in a source protected routine seems like the simplest solution. A person with the correct protection key could edit the rung online, while others could only view the values.
 
I would go with source protection rather than AIO, If you put them into an AOI, you are going to have to download every time you want to make changes.
 

Similar Topics

Hello, PLCS.net guys. Currently I'm making the safety communication on 1756-DNB to DX200 Yaskawa contoller. I made the setting and assigned the...
Replies
2
Views
603
When I installed my RS Logix to another computer version 18 and I went online and tried to look at the properties of the 1756-IF6CS it would no...
Replies
1
Views
1,142
Hi All, This topic it is really interesting indeed. Hi have a doubt that is inside this kind of questions: RSLogix 5k V28, 1756-L73CPU value...