Can't add EN2T D ver 10.6

dahnuguy

Member
Join Date
Mar 2007
Location
SC
Posts
720
Searched on AB website for eds file.
http://www.ab.com/networks/eds/cgi-bin/search.cgi

There is no 1756-EN2T D

This is what is listed:

Rockwell Automation/Allen-Bradley Details | Download Communication Adapter 1756-EN2TP 1756-EN2TP 10 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2T 1756-EN2T 2 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2T 1756-EN2T 3 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2T 1756-EN2T 4 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2T 1756-EN2T 5 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2T 1756-EN2T 10 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2T/A 1756-EN2T/A 1 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2TR 1756-EN2TR 2 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2TR 1756-EN2TR 4 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2TR 1756-EN2TR 5 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2TR 1756-EN2TR 10 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2TSC 1756-EN2TSC 5 1
Allen-Bradley Details | Download Communications Adapter 1756-EN2TSC 1756-EN2TSC 10 1


So I downloaded all the EN2T files with a version 10 and installed them in RSLogix5000 using the eds tool.

I think this is the correct eds file, but not sure: 0001000C00A60A00.eds


I still have the yellow question mark in the hardware config of the project.
Right click backplane in HW congif tree and select discover.
...and RS discovers all the EN2T ver 10.6 in the rack and they seem to be correctly identified. "no action needed"

Still have yellow question mark in project tree and can not go to properties of device.

Try to add a new EN2T, and the version tab only allows up to version 5.
As if no eds files were added.

Closed everything and rebooted twice, went to get water, did 2 spins for Tuesday. Twos day...

Still doesn't work, no change.

Everything is fine with other RSLogics install on other PC, so I know it is a "simple" eds issue.

Any ideas?
 
Yup; with A-B communication modules you need more than an EDS. To make the v10 firmware (that's the Series D modules) available in Studio 5000, you need to download and execute the Add-On Profile (AOP) installer.

RA Knowledgebase Article 575816 (Access Level: Everyone) shows you all the steps for those modules.
 
RA Knowledgebase Article 575816 (Access Level: Everyone) shows you all the steps for those modules.[/QUOTE]

Knowledgebase / Forum Registration Incomplete
If you just saved your profile, please wait up to 15 minutes while our systems process your request and send you an email confirming your registration. You will not be able to log in until you have received this email, clicked the "Verify My Email Address" link, then logged in and completed your profile.

The email I received from rockwell has no link to verify my email so I am stuck at this point.

I think I can manage from here though. As long as adding the Addon is terribly complex.



Thanks for the responses.
 
I don't know why, but the new-user registration has been broken for weeks. If they still don't come through with a confirmation e-mail, gather your patience and call on the phone tomorrow.
 

Similar Topics

Im trying to create a level indicator for water Tank i have used the ADD function while the pump is on and level increasing everything works...
Replies
14
Views
102
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
418
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
1
Views
113
PLC: Fx5u CPU As Per manual High Speed Input Module can add from Navigation window  [Parameter]  [Module Information]  Right-click  [Add New...
Replies
1
Views
71
Back
Top Bottom