I’m looking for, and I can’t seem to find, a sensor or transducer that will give me a reading of pressure applied to an object. Squeezing or clamped pressure is what I’m trying to achieve. It’s going into an ML1400 and it could be a 4-20ma signal or a 10-30v signal, either could be worked with.
 
as RDS said, look at load cells.

most all load cells are mv/volt excitation, so you will need an amplifier.
you can buy them 0-10v or 4-20ma.

CAUTION - this is from experience.

what is your application?
I say that because load cells are subject to destruction from load shock.
applying a load to a load cell is one thing, applying a sudden grip load is another story.

sudden application of a force to the load cell will result in an impact load of 6-10 times what the load sees after it settles (2-3 seconds later).

for example, picking up a 25 lb weight using an air cylinder even 1 inch at what I considered a slow rate caused the load cell to fail after a month.

we had to use a 250 lb load cell. we soon learned to increase our load cell capacity by a factor of 6 to 10.

james
 
as RDS said, look at load cells.

most all load cells are mv/volt excitation, so you will need an amplifier.
you can buy them 0-10v or 4-20ma.

CAUTION - this is from experience.

what is your application?
I say that because load cells are subject to destruction from load shock.
applying a load to a load cell is one thing, applying a sudden grip load is another story.

sudden application of a force to the load cell will result in an impact load of 6-10 times what the load sees after it settles (2-3 seconds later).

for example, picking up a 25 lb weight using an air cylinder even 1 inch at what I considered a slow rate caused the load cell to fail after a month.

we had to use a 250 lb load cell. we soon learned to increase our load cell capacity by a factor of 6 to 10.

james

The force applied won’t be sudden. The load is driven by a screw and I want to make a safety provision in the machine to make sure that the force applied to the object that is being clamped stays “clamped” during operation. If the clamp were to loosen up during machine use I want to set something up in the logic that will stop the machine so that things don’t go flying all over. I’ll look into what was suggested above tonight, thanks all
 

Similar Topics

Hi, I am looking into a project to build a control system for a hydraulic test machine. Working with hydraulics is not something I have done...
Replies
10
Views
3,540
I need to ramp up the psi on a pnuematic cylinder until the force on the piston, measured by a load cell, is met. Then I need the air pressure to...
Replies
9
Views
4,514
Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
Replies
3
Views
138
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
80
Hello all, I have a question in regards to RSlogix 5000. I am having issues with the program force closing when I try to make online edits. We...
Replies
0
Views
95
Back
Top Bottom