How far in wire feet is the motor from the drive? Since this is a PF4, it's probably low hp which can be very susseptible to lead capacitance currents causing faulting.

And, follow OkiePC's advice on this exactly. Anything less than a 1000V megger is not going to help you. And use it to check phase-to-phase, not just phase-to-ground.