PowerFlex 753 OL Current Protection?
Ih8Siemens
Dec 2017
Unknown
52
Hey fellas,
Been getting absolutely hammered this week with tons of cool and exciting new weird problems so here's another one that I believe I know the answer but would love some other ideas.
The customer has 2 Powerflex 753 VFD's individually controlling 2 motors that operate their own tri plex plunger pumps. (PID controls speed reference for 1, if 1 cant reach setpoint after x amount of time a seperate PID controls both) but we haven't got to the fun of tuning that yet.
We start the first ~325 HP motor and tested it full speed with no problems.
we start the second one (~250HP) by itself and ran it full speed with no problems.
When we start both motors and set them to 44hz the bigger motor's powerflex drops down to 33hz on an OL current fault/alarm.
The only thing I can think of that could cause this is a spike in pressure which forces the drive to work harder? Its getting ~900psi on the discharge line but I almost want to say that the motor is undersized for the application. all the name plate information is correct in the drive, power is all good, I really cant find another explanation for this. Just want to collect a few more ideas before I respond to the customer that they need a new shiny expensive motor.
Thanks for the help fellas,
Yeah, the only thing I can think is exactly what you're suggesting- the load becomes too high for the motors when both pumps are on at the same time.
Only other thing could be if the feeder isn't sized right, the voltage could be sagging when both are on at the same time, raising the amp draw.
I didn't even think of that....I will have the electricians on site check it out tomorrow.
***Update***
The motor was in fact under sized.... Someone is taking an *** chewing.
Hi everyone, I have a AB Powerflex 753 powering a simple 480V permanent magnet motor using flux vector control (I believe it's the only control...
1,325
Hi guys, We have an Allen Bradley Powerflex 753 drive powering a simple blower (37kW) motor which we have just powered up. At 50Hz the blower is...
23
8,073
Hello everybody, I am connecting my DCS digital output (115VAC) to AB PowerFlex 753 Digital Input. We are using the 20-750-2262D-2R I/O option...
4,875
How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
100
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
1,330