Siemens connection help
the_msp
May 2008
Northern Ireland
1,271
Hello, I am trying to connect to the following PLC s7-300. The PLC is in a box that takes 1/2 hour to remove from the line and ideally I need to connect when it is in situ, connected to its sensors.
There is a ProfiBus looking cable connected to the port labelled MPI, this goes to an HMI and a service port which has 3 leads soldered.
Using the attached MPI lead will I be able to connect via the service port?
Can I upload the program albeit with no comments?
TIA
Yes, you should be able to.
You'll have to configure the USB adapter (that's what that device will be called when you install it) and connect to either the MPI port or the Other port which seems to be a Profibus connection.
OK, thanks, and I can connect the end of the USB adapter lead into the service port ok? I can't directly plug it into X1 on the CPU, no access when machine is connected...
Find the other end of the cables... you may have one that will have a open port and you can just plug into it there, then you do not have to remove any you can just jump onto the network
You can also watch this video, its for our aftermarket but should be close enough for you to be able to do the same
https://www.youtube.com/watch?v=skAH715dPxM
The other end of the cable may look like this and you can just plug into it
I know the other (MPI) end. Service port -> X1 -> HMI
The DP goes to the main (S7-400) CPU, I don't think I have an adapter to get onto it.
Thanks for video link :)
Check to see if the 400 has a connection of the one similar to the pic I posted, most of the time you can just plug in and you dont need to unplug anything... also the HMI may have a double ended plug
Been fighting all morning with a stubborn HMI. It just won´t connect with the plc. attaching from settings. Have i missed anything? Both plc and...
235
Hi, I have a plant where we recently changed CPUs from 315-2DP to 315 -2PN/DP. They are all connected to a Beijer panel. Strange thing is that...
1,183
Hi Experts, One of our clients, until recently, could connect remotely via the internet to a Siemens TP1200 Comfort HMI via VNC and **** Cosy...
1,535
Good afternoon! Please help, the following situation happened: Connected encoder Siemens 6FX2001-5QN25 with Profinet IO to PLC S7-1200. The...
1,065
Ye..llow everyone! I need some help on this: I have TIA project with an Siemens HMI connected to an OPC server. This HMI has the file name...
956
