S5-95U analog output
MRM
Dec 2017
Algeria
I m new in STEP 5 and i need help
I have problem with the onboard's analog output 4-20mA, i want to forced it to see if it work or not but i didn't find the assignement in S5 Program. As i know, normally it's in FB251( XE)
SPA FB 251
XE : MW 12
BG : KF +8
KNKT: KY 0,0
OGR : KF +1000
UGR : KF +0
FEH : M 2.1
BU : M 2.2
i forced MW 12 but no signal!!
Please i need help
i checked the assignement list now there is no AW or QW, all are memory assignement or digital I/O
MW 12 used only on this
SPA FB 251
XE : MW 12
BG : KF +8
KNKT: KY 0,0
OGR : KF +1000
UGR : KF +0
FEH : M 2.1
BU : M 2.2
A DB 20
L DW 48
T MW 10
A DB 21
L DW 48
T MW 12
A DB 22
L DW 48
T MW 14
BE
one is onboard analog output and the other two are for the external analog module
The analog output is normally QW40.
Monitor this value directly and then "force" MW12 (dont forget to block the existing T MW12)
JRW
That is possible and the error bit(s) will come on as well
Without the program not sure if these error bits are used to indicate faults, stop the machine etc.........
I tried L KF +500
when I measured the output, I found -74 mA
can you told me what is the problem ? and what i have to do ?
thank you very much in advance for your help
I have the above CPU. I need to check if the onboard I/O are working. I am viewing it on line with Step 5. I have a manual for it, it has eight AI...
4,367
I have a system with this PLC and there are 8 analog input devices connected to the onboard A/I terminals. In the program, I can only find PW40...
2,918
I would like to know if it is possible to read from an analog sensor 0-5 V with an analog module input of a s5-95u. I sow in the manual that this...
2,196
Hi there! This is something so old and having machine with it....... Last time unit was powered around 3yr ago and it did not work since than...
193
Hi All, We have a hydraulic press that is being controlled by Siemens S5-95U PLC . Lately the S5-95U has been randomly stopping during operation...
2,383