cellular data usage

abishur

Member
Join Date
May 2012
Location
Texas
Posts
47
I'm trying to calculate how much data I might need. Rather than monitoring a remote device, I need to be able to connect to the PLC (either an Allen-Bradley CompactLogix or a Schneider-Electric M340)over a cell modem using the programming software (RSLogix5000 or Unity). Has anyone done this in the past who could estimate how much data is used while being connected to a PLC by the programming software?
 
Those links do a good job breaking down costs when using a cell modem to monitor a PLC from an HMI, but not so much the data used by the programming software.

I have access to some Schneider PLCs so I used Netlimiter 4 to do some active tests and see the data I used and discovered the following (If anyone could do this same kind of test using a Rockwell PLC and RSLogix 5000, I'd be very thankful):

1)When doing a slightly exaggerated number of compiles, 25 MB an hour is a fairly reasonable estimation of data use.

2) The more data shown on the screen (i.e. if you're zoomed out) the more data Unity will use (showing a reasonable amount of data resulted in ~3.04 KB/s UP from the PLC and 709 B/S DOWN to the PLC, whereas showing an entire FBD section with lots of data was practically 7 KB/s UP from the PLC!)

3)Sections sitting in the background consume Data!

4)Closing unused screens and turning off

5) Animation Tables used less data than the same amount of objects being viewed within a section. (1.6 KB/s in the actual section and 970 B/s in the animation table.

So if I left the animations off as much as possible, kept only 1 section open at a time, and grouped my compiles together when possible I could shave a good deal off the 25 MB/hr, but who's actually going to do that?
 

Similar Topics

Hey guys, I have an SE deployment at a plant where it is monitoring several remote sites that utilize cellular modems for internet connectivity...
Replies
2
Views
1,988
Hi all, I have a client that has a water tank with a loop powered level sensor; the 4-20mA loop goes through a telephone line, half a mile away...
Replies
26
Views
6,933
Hi, I have a flow meter which needs to be connected to our SCADA via GPRS/GSM/4G or any cellular type RTU's If any one have an idea please share...
Replies
7
Views
2,475
Hello, We are looking at setting up some machines in another country where internet is not available. We could use some cellular service where...
Replies
1
Views
1,288
I'm using ICX HWC35 cellular gateway with Allen Bradley 1769 L33ER PLC for messaging purpose Already upload the AOI instruction to the project...
Replies
3
Views
4,390
Back
Top Bottom