Siemens Simatic TI505
Plastic
Feb 2009
Michigan
319
Stick a fork in it?
Circa 1995 control system on a critical machine. Less than 100 Digital IO, less than 10 analog IO.
I believe we can remove the TI rack and jack in AB 1734 point IO in that same footprint.
With having a CompactLogix PLC pre-programmed, I think we could pull off a retrofit in a weekend.
Any other thoughts on this?
Plastic
Stick a fork in it?
Plastic
I've done TI500 to AB and TI500 to TI505 quite a while back. Yes it can be done in a weekend.
BUT make sure you understand the 505 program and as JRW mentioned look for any special function routines.
THEN test the heck out of the AB. Lest you get bit by ASSuming how the TI works.
You might also leave an out for going back if things get really mucked up.
Any special function programs running in it ?
Why yes, there is a Delta TMC card in the Siemens rack. We will migrate that to a Delta RMC75-E. We are having great success with the RMC. The Delta is for Velocity and Pressure control of one of the machine axis. We will change to position transduce to SSI, and change the hydraulic actuator valve to a 2017 era valve.
Thank you for feedback about special TI functions, we think we understand the machine requirements more than we need to know how a TI505 functions, but our ears are open to all input, and valued experiences.
Plastic
The only thing that burnt me once was I had a few programs that relied on 'last output state' wins in the TI505s.
So I wouldn't copy the logic, I'd just rewrite it into a modern structure.
Hi. I have 2 files where I would like to see the ladder logic differences (similar to the Rockwell compare function). I am using TISoft Siemens...
1,251
Hi, I am currently looking at having to convert a SIEMENS SIAMTIC TI505 plc into an AB PLC. Let me start this off by saying I don't know much...
17
16,358
Hi there, this is my first post so please let me know if I'm doing anything wrong! I have a surplus Siemens Simatic TI505 Rack with a number of...
3,862
Gents, I am replacing: 1EA - Siemens Simatic TI505-6660, Processor 1EA - TI545-1101, Power Supply 5EA - 24VDC Input Card 3EA - 1/2A DC Output...
4,558
Good Evening , It has been several years since I used Siemens Software . I’m looking to purchase the software for a Siemens Simatic S7...
471