AB FLEX IO Limits
AJZ
Jul 2003
Ontario
265
What are the limits for module use on a AB 1794 FLEX IO system?
I know that the maximum number of modules is eight and the maximum number of I/O points is 256. Based on this info, I can use eight 32point modules. Is that correct?
Also, is there a limitation to the number of input or output modules used?. For example, can I use six 1794-IB32 modules with two 1794-OB32 modules
Adrian
Disclaimer; I have not worked directly with the 32-point I/O modules but I am very familiar with the fundamentals of the 1794 platform.
The physical FLEX bus can support eight modules of any type. Analog, Specialty, 8-point, 16-point, or 32-point, it doesn't matter.
1794 FLEX is a 16-bit I/O architecture, so if you have 32-point modules you will have to logically communicate with them differently than with 16-point ones.
The most important consideration is which network adapter you are going to choose. Only the newest adapters for RIO, DeviceNet, ControlNet, and EtherNet/IP support the 32-point I/O modules, and they do so in slightly different ways.
The EtherNet/IP adapter, for example, allows you to make a logical I/O connection directly to the 32-point module, which is less efficient than a "rack optimized" connection but still works. I think the RIO adapter requires block transfers.
Get the release notes for the network adapter you will be using and they will have information on how 32-bit support is implemented in that adapter.
Here's a 32-bit module compatiblity table, taken from the 1794-IB32 installation manual:
Remote I/O
1794-ASB series E or later
1794-ASB2 series D or later
ControlNet
1794-ACN15 series C, firmware revision 4.1 or later
1794-ACNR15 series C, firmware revision 4.1 or later
Ethernet
1794-AENT series A, firmware revision 2.4 or later
PROFIBUS
1794-APB series A, version 1.1 of the GSD file
ControlLogixTM Family RSLogix5000 programming software, version 11 or later
Just want to confirm that Ken is correct.
Limit still 8 modules.
Correct adapter must be used that supports 32 bit mode.
Thanks, Ken.
I am working on a new system using DeviceNet as the Network. A CLX L61 is the PLC.
Ken, I noticed that you did not list a DeviceNet module in your list. Does that mean I cannot use the 32point modules?
Adrian
Check these technotes for 32 point modules and 1794-ADN:
P20842 - 1794OB32P, 1794IB32, 32 point Flex I/O module and supported adapters.
Q110737688 - DeviceNet: 1794-ADN f/w 2.002 issue with Autoscan and 1794-IB32 or 1794-OB32P
A63745719 - Configuring 32 point discrete Flex I/O on a 1794-ADN DeviceNet adapter
Thanks for those, Control_Conn.
Those knowbase articles are more thorough than the installation instructions that I downloaded. See what happens when we let literature majors do engineer's work ! :)
FLEX is a pretty old architecture and I'm grumpy about the way it works on DeviceNet (complex to map and maintain), but it's a good way to get a lot of I/O in a small space, especially when you connect it up on ControlNet or EtherNet/IP.
Hi How do I configure high and low limits for a number entry I know I can program limits in the PLC to catch this. I have looked into WinCC and...
5,491
Hello everyone, my son and I are working on building a metal lathe. I been waiting for a motor/speed controller donor from a treadmill. I finally...