You probably need to set the "Point Mode" for the input points in the software?
Without this set the inputs will be inactive.

Go the the module properties for the 1734-IB8S and then to the "Input configuration" tab.

Under "Point Mode", select the Safety function for the individual input points.

Usually for a light curtain or similar you will select "Safety".

You also setup for Single or Dual function here with "Point Operation".