Rounding off on the migration stuff, one more help please.
IdealDan
May 2017
MA
480
So far so good, Almost done with this migration stuff
Someone please help me on this one:
ERROR IS:
''Bit and LSBit triggered alarms that used a Trigger Tag with a Bit data type will only be able to trigger a single alarm after import.''
Who can help give me an ideal of the right correction to this log error?
If it's a single bit trigger, no problem. Change the tag to a Bool type in the tag database.
Then use analog trigger in the Alarm setup, value 1 in the messages tab.
If it's a LSBit, then you need to change the tag to an Integer type. Now you can create a bit array in the Alarm trigger using LSBit.
Open the FactoryTalk View ME Help and search for topic "About array tags"
In either case, you will want to look at that tag in PanelBuilder and see how it was configured. Watch out for a bit array that starts in the middle of the word (ex. it does not starts at 0). Those you may not be able to convert exactly the same.
Thanks Dear. and remain blessed. I will try that right away!
I have a Beckhoff PLC with many AI modules. Most devices are loop powered using the same +24 VDC power as the Beckhoff Bus Coupler and all is...
665
Dear All, I need to round off the analog value FOR EXAMPLE: 123.45 to 123 Please prove solution. Thanks
20,811
Hi all,Is anyone able to help me with a method for rounding off a value following a division instruction. I am using Siemens S7 and plan to...
3,366
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
266
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
433