1769-AENTR Fault Control
PerryMB
Jul 2010
Maryland
I have 1769-L35E CompactLogix controller communicating to two 1769-AENTR. While testing, I can pull the Ethernet cable and I get a major fault. Does anyone know of way to turn this feature off so I can use logic to determine if I have a communication problem?
Thanks,
Welcome to the PLCTalk Forum community !
Look at the Connection tab for the 1769-AENTR in the Studio 5000 I/O tree. There is a checkbox for "Major Fault on Controller if Connection Fails in Run Mode".
It's probably checked in your system, so un-check it. You can do so online in Run mode.
Have a look through the Forum or the RA Knowledgebase on how to use GSV instructions to detect I/O connection status.
Double click on the 1769-AENTR in the I/O tree. On the connection tab you can select if you want to Major fault the CPU or not.
Thanks for all the replies.
I do have the check boxes unchecked.
I don't have direct experience with the 1769-AENTR but I believe that it bridges a module connection to each of the 31 possible connected modules, rather than using a "rack optimized" connection like the 1734-AENT or 1756-ENBT can.
So check the Connection tab for each of the connected 1769 modules connected to each Adapter.
If all that doesn't work, trigger the fault and review the fault code and we'll see if it points us toward a different root cause.
Ken,
I checked connection tab on each input and output card and they had the Major Fault check. I assume that connection tab on the 1769-AENTR would determine if a fault would happen. You know what they say about assuming.
Thanks for the tip.
GSV and AENTR
OK this may or may not be a good place for this question. I have approximately 10 AENTR units and each has a web page that one could look at. I noticed that there are error counters and other really cool information. This is not about that.
So when we start loosing information we would like to see the error counters or information that tells me that the Ethernet connection is about to be dropped out.
With Remote I/O we had a bunch of counters that could be monitored and based on the retry numbers we could say "Clean your wire path"
So with a GSV instruction we can see if a module has failed or if the status of the lights but what about retry counters or missed communication or packet errors, is there a way to read these from my modules ???
Forgot to mention there are sliprings involved and I need a way that lets me know that oxidation is starting to effect my data. Hence "Clean your wire path"
Hi all, I have recently upgraded a PLC 5 to a 1769-L33ER and 1769-AENTR. It is two panels, back to back, with the L33ER in one, and the AENTR in...
3,615
Hi everyone, I recently put in a 1769-AENTR, and where it is installed has had a couple power outages. Every time when the PLC comes back online...
682
Dear All, If you could please help me with the following issue it would be very helpful. Trying to solve this for the last week. I've a L33ERM...
1,230
Is anyone else watching AB 1769 1794 1734 pricing on ebay, or am i the only one??? 1769 AENTR for $4,000.........From China........Its getting...
2,023
3x 1769-AENTR being polled by 5069-L330ER PLC. AENT modules are freezing approx once per day each. Loss of communications from perspective of...
1,658