How to calculate the Accuracy of Pressure Transmitter and rtd's
jcp
Feb 2010
Multan
369
Hi friends;
I done the calibration of pressure transmitters and rtd's.
I give one example of data for both plz guide me how i calculate the accuracy of the transmitter and RTD's.
Pressure transmitter:
Range 0 to 200" w.c
signal applied reading
0 0
50 51
100 101
150 151
200 201
The error is 1"w.c how i calculate the accuracy?
RTD's example
32 32
100 101
150 152
200 203
Now how i calculate the RTD accuracy while i used PT100 RTD.
PLz help me?
For the pressure transmitter, the range is 0-200" for a span of 200".
An error of 1" over 200" is 1/200 or 0.5%
For the RTD, the range is 32-200° or 168°
An error of 3° over a span of 168° is 3/168 or 1.8%
Just make sure that whomever you give the information to understands what you are giving them.
Other things that effect overall accuracy are temperature and hysteresis. Some manufacturers lump all effects into a single value, others list them all separately. Just make sure you give enough information with your accuracy so the person using it can use the information properly.
[FONT=&quot]Accuracy = (Deviation / Span ) * 100[/FONT]
[FONT=&quot]Deviation = Expected Value - Actual Value
Since you said "Transmitter" and "Data" be sure you differentiate between sensor values and analog output values. That and 5 point checks up and down and you should be good
[/FONT]
calcs by danw are correct, however you also have the accuracy of the testsignal and its reading.
if you are using steaming water the pressure of the air is important, just like with pressure readings.
18
929
Good morning, I have a question. I don't know much about ST yet I would like to calculate the average number of products per hour. how do I do...
22
2,931
Can someone help me with this? I'm no good at SCL - virtually everything I've done so far has been ladder logic. The return value from the...
1,095
I want to calculate the energy consumed from instantaneous power. Can this be done using the TOT block with timebase set to Hour?
675
Hi everyone, I have to calculate the length in millimeters of a glass that enters a transport (I don't know the speed yet) through a barrier...
3,452