Scale Analogue
richleva
Sep 2012
ontario
79
Hello,
I'm confused with Instruction called "SCP" with RSlogix. Never really had to use this one, till now.
I need to control an Acid pump at a water treatment plant, Using an analogue output of a PLC. This PLC only has 0-10V analogue output card. So I was going to install a 500Ohm resister to get my 4-20Ma. So at 2Votls will be my 4mA and 10 Volts will be 20mA
If the pump for example is 0-37 liter/hour
I assume the:
Input min is 0
Input Max is 37
How do I figure the Scaled Min and Scaled Max?
Also remembering that 2 Volts should be 4mA
Thanks everyone
If it were me I would scale the output of the pump to another variable in mA desired. Then use another block to scale the mA to the V.
It will make it easier for the next guy, especially as you can comment the rung, it makes it easy on the eye to what you have done.
So 0 to 37 scales to 4 to 20 then 4 to 20 then scales to say 2000 to 10000, 6554 to 32767 on your OP card (or whatever units it is set for)
Hi Janner,
What do you mean by (6554 to 32767 on your OP card)?
Taken from manual:
Number of inputs 2 single-ended
Voltage output range 0…10 V DC - 1 LSB
Type of data 12 bit unsigned integer
Step response 2.5 ms @ 95%
Load range Voltage output >1 KΩ
Output coding (0…10V DC) 0…4095
Output resolution 12 bit
Analog output setting time 3 ms (max.)
Overall Accuracy
-20…60 °C (-4…140 °F) ±1.0% of full scale
Electrical isolation Non-isolated with internal logic
Cable length 30 m (98 ft) shielded cable
So your 2v to 10v output would be 819 - 4095.
Something like this:
Hello,
/QUOTE]
Your acid pump is also a load on the circuit. What is it's value?
You are better off using a converter to convert voltage to current.
See link(s) for an example..
https://www.automationdirect.com/ad...Voltage,_Current_or_Potentiometer_Input/FC-33
https://www.google.com/search?rlz=1...HZAhWJ8YMKHc_XC9QQ1QIItgEoAQ&biw=1671&bih=830
Taken from manual:
Overall Accuracy
Only one "SCP" is required. First one with scaled min/max at 819-4095.
FYI: the ML1400 will not allow two "SCP"'s on the same rung. It uses RSLogix500 not RSLogix5000.
Should have said on the same rung in series, parallel would be ok.
I have an extremely dumb math question. An analogue input gives me 0 to 27648 when operating in 0 to 20mA In the program I want to scale into...
4,334
the scale occasionally stops working and displays the message "no response from modbus" on the control screen . tunaylar - load line2
139
Hi! I'm wondering if PLCs are used for small-scale production. I've got four machines doing different things with textiles, and I'm exploring the...
16
1,335
I am having an issue writing a carriage return to my scale, I can manually push the print button the the scale and then read the buffer. The scale...
1,113
Good afternoon. 1794-ie12 module available, channel set to 4...20 mA. According to the table from the manual, we get from 0 at 4mA to 30840 at...
2,255