choosing capacitor when translate 3 phase AC motor into single phase
alezi
Dec 2005
Nova Payova
Hello colleagues,
How it is go on, I have one question, maybe simple for some experts, I need to know, how calculate which capacitor we are need when transformed 3 phase AC motor in single phase motor, I know one formula C= 70 √P, when is C in metric units micro F(Farads) and P is power from AC motor in W(Watt),
in example: P=100w
when computing we are to receive very strange results approximately 700 micro F, of course I’m informed about chart for choose volume capacitors.
Thank you for replay
Aleksandar
Hi Aleksander ,
Your question is not clear
Please explain what you are trying to do
You can run a single phase motor from a 3 phase supply if you have a suitable/safe means of connecting it to a local distribution board
Not sure why you are requiring to connect capacitors unless you need to provide power factor correction
more information please
Aleksandar
The above formula is unknown to me, and when I do a google search I also find no formula like it or even similar.
We need alot more detail if you would like us to assist you.
alezi said:
Hello colleagues,
in example: P=100w
when computing we are to receive very strange results approximately 700 micro F, of course I’m informed about chart for choose volume capacitors. Thank you for replay Aleksandar
Most confusing.
Are you trying to run a single phase motor off 3 phase and need to know the capacitor value for the motor?
ANSWER Look on the nameplate or call the factory.
Are you trying to run a 3 phase motor on single phase?
ANSWER There have been several methods to do this - you can still do any of them. BUT if motor is
3 HP or less you can get VFD to run off 120 single phase
50 HP or less you can get VFD to run off 230 single phase
WITH much less hassle and LESS or maybe equal cost.
Dan Bentler
You will not achieve satisfactory results trying to run a three phase motor on only single phase with a capacitor. However, if you add a second motor as an idler motor with a small capacitor to get the second motor started, then you can achieve some marginal results. The idler motor will generate your third phase, however you won't have the motor full rated power. This set up is called a rotary phase converter, and if you search google.com for rotary phase converter you can find many websites with detailed instructions on how to set one upand how to size the ilder motor and the capacitor. For general purpose three phase motors and three phase motors on simple machine tools this is an economical and frequently used alternative.
More expensive options are VFDs and motor/generator sets.
You can run a small (personally had good results up to 0.75kW) 3-phase motor on a single phase net by simply adding a running capacitor.
C = 70 x kW (formula for 230/400V 50Hz 3-phase motors to run on a 230V 50Hz single phase supply)
For example a 0.37kW motor would require a 25µF cap.
You'll have to keep in mind that starting torque drops dramatically, but for pumps or other low starting torque applications it is a simple and effective solution (so forget about running an 3-phase air compressor).
Hope this helps
Sparkz, where do you connect the capacitor? What do you connect to the remaining motor phase wire?
Vsd
Why not use a single phase to three phase frequency drive, should simply need to connect the motor in Delta instead of star. I have several of htese onsite and they are valiable from a variety of suppliers I use SEW and AB.
Cheers
Peter
On this side of the pond, if the motor is 3 phase star 400V connected then you would connect single phase to 2 legs of the winding in delta and put a capacitor across L and the other delta leg. Dont know if the C value is correct ( i have it at work somewhere ) its a really crude method of running a 3 phase motor on single phase, no starting torque and some motors dont like it and overheat, Normally called Steinmetz Connection from memory and i have even seen this (we do motor rewinds) on OEM manufacturer machinery!
Real crappy in my opinion....
Hi Lancie,
Dave beat me to it in answering your question... but also Peter has a good point.
Nowadays the cap solution is only used for economical reasons: A perm cap costs around €5 to €10, while a VFD costs about twenty times as much. On the other hand, you wouldn't have to worry about torque when using a VFD, so you could run any application (up to 3kW I think?) on a single phase.
BTW, the Steinmetz connection has been around for decades, way before there were "fancy" VFD's ;-)
To Dave: We also do motor rewinds (dad started back in the late 60's).
Thanks a lot for respond every body, some people think this is wonder because today we are have many ways for solve this problem like as vfd, problem is money ,one permanent capacitors is much chipper then vfd,I know all about loosing power and moment inertia when three phase motor work like single phase, when motor give us enough power it is better solution, money we are spend on others things.
And again thanks for replay,
Aleksandar
Good evening, I'm primarily a Siemens user, but I have an incoming project where I need to use Allen Bradley everything. So far I know that the...
2,634
Hello, I am trying to choose from 4 different tank levels (REAL) and choose the greatest number (highest) and set that to open that tanks valve...
1,877
I am going to daisy chain a couple Modbus devices off of a Click plc using rs 485. There will be three slave devices daisy chained off one another...
16
9,167
Good day all. I work for a small company that would like to start automating the production of our goods. I have been tasked with doing some...
49
13,524
I'm trying to remember the lessons for replacing a SLC CPU, but I so rarely have to do it, I'm afraid of screwing it up. I'm hoping to give my...
2,477