UL Class 2 Circuits
theColonel26
Feb 2014
West Michigan
784
Ok am finding UL 508a section 44 rather vague....
Does the Power supply that supplies a Class 2 Circuit have to be Listed for UL Class 2?
If No
Does the Power Supply have to be limited to 100W output?
Or
If I use fast blow fuses to limit circuits to less than 100W. Are those circuits Class 2 then?
If the panel will be inspected for listing make your life simple. Use a class 2 power supply.
There are several available.
The class 2 rated power supplies have circuits that guarantee power limiting above what regular power supplies have.
Well I would need a like 3 separate Class 2 power supplies instead of 1 240W power supply.....
Do most people just use more than one power supply if then need more than 100W?
That also takes up a lot of room
My recollection from talking to our UL inspector was that fusing down to <100W was sufficient.
:geek: thank you
And the above is wrong. Class 2 is limited to 100 ma. Either a class 2 power supply, or class 2 converter. Something like a 1692 ELP.
Fusing doesn’t cut it per UL.
And yes, I often have a class 2 power supply in addition to say a 240W power supply.
Cheers!
Cheers!
100 milli Amps... ?
Sorry, 100VA (aka watts.) 3.8A, 24Vdc is typical.
Apologies for not answering your initial question. Yes, it needs to be listed as a UL class 2 power supply.
Remind me not to post after drinking….
ok that is what I figured you meant just wanted to check :oops:
:beer:Where is the fun in that?
Use a 240W power supply. Then use a class 2 electronic circuit breaker such as the Allen Bradley 1692 series or Siemens Selectivity modules. Depending on the module, you can usually get 4 class 2 circuits from one.
There are other companies that make them as well - and I believe Automation Direct may have a new electronic circuit breaker - not sure what it is though.
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
106
I'm looking for some clarification if anyone here is familiar with UL698a panels. Panel is out of zone/class'd area. with thermocouples extending...
113
Hi, im facing an issue to change the alarm level into another state in the alarm class configuration in Cimplicity. Im trying to change the...
468
Hi - I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing...
967
I'm working on getting a handful of devices hooked up to an EWEB card on an Allen-Bradley 1756 PLC using the Ethernet/IP socket interface, and...
2,018