TIA V13 Controlling Drive from S7-300
file sent
In this example i selected PPO2 and there are input and output addresses , what are these ?
are these set automatically ?
when reading from the slave which addresses i use and similarly for writing to slave which addresses i use ??
PPO2 uses 6 works of process data PZD and 4 words of parameter data PKW.
What parameter data or P's in the masterdrive do you need to write to?
And why?
PPO2 uses 6 works of process data PKW and 4 words of parameter data PZD.
And why?
i want to send a control word , a speed set point and Torque limit to the drive
after that i receive six values from drive which will be actual speed , actual torque , status word , dc bus voltage and two more , i will display these on an HMI will work on that part once i can run the drive
Hello
in the DPRD_DAT
Record := P#DIX98.0 BYTE 12
Please explain the part in Bold , is it pointing to the Data block ? data blocks are addressed as DB but here it is DIX , and what does 98 means in DIX98
I should wait for JRW to answer, but this is a pointer, addressing internal bytes of the DB that is currently opened.
I studied the Program and found answer to my question ,
This is an instant DB tied to a function block and the data (DPRD_DAT) is saved starting from offset 98.0 and further to 12 byte starting from there
I am trying to write the same program and I find that when I add more local variables the offset keeps changing and therefore either i should define all the local variables before i start writing the code in FB or i can change the address (where to save the control word and rest of the PZD ) once i am finished with the Program .
JRW, can you please explain this ? the bits are not sequenced as they appear in the Control word ,
CALL DPWR_DAT
LADDR :=#DriveAddr
RECORD :=P#DIX86.0 BYTE 12
but the write instruction will write 12 bytes starting from offset 86.0
I believe the control word Bits are specific and each bit mean something and what they represent can not be changed
  • Control Word.pdf
I am working on a program that was developed in 2015 for an S7-300 safety PLC. The new copy of this machine uses an S7-1500 safety plc. We were...
1,868
Hi Guys, Please, I'm in need of TIA Portal v13 SP1 The V13 I saw can't open a Comfort panel HMI file. Can any one help? It will be much...
5,374
Hey guys, So I successfully added a new Leuze barcode scanner to my existing profinet network and now I'm trying to add HW_Submodules to my new...
3,285
Hey guys, so I'm having issues going online with a plc using TIA V13. I feel like I must be missing something basic in my understanding. New to...
1,882
Trying to add new logic using TIA V13 and when I try to download I get this message that I attached. This machine is running constantly. Will I...
2,007